• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Panic Hardware

Kendra

Registered User
Joined
Aug 25, 2017
Messages
70
Location
Philadelphia
I am working on a vestibule for a commercial building. The vestibule will serve two tenant spaces. One has an occupancy load of 25 and on has an occupancy load of 68. Both are group B occupancy types. There are individual doors coming into the vesitbule from each space, does this vestibule have to have panic hardware?
 
No, the doors serve neither Group A nor Group E occupancies. The space with an occupant load of 68 will need to have a second means of egress, which means the occupant load egressing through the vestibule will be 34 occupants plus the 25 occupants from the other tenant space (59 total). The door will need to swing out-ward, though.
 