Penetrations in a non-rated wall are not required to be protected. Even if the wall is required to be protected per the construction type (e.g., Type VA, which requires 1-hour construction for bearing walls), it is not required to have protected penetrations or openings (this, however, does not apply to horizontal assemblies)--only the four rated wall assemblies (fire walls, fire barriers, fire partitions, and smoke barriers) are required to have protected openings. Smoke partitions will only need to have systems that meet the leakage requirements of Section 710.