There have been building scientists pushing an exterior cladding system developed in Canada called "PERSIST", it is being used in the Eastern portions of the United States apparently without objection by the local building departments. Here is a good simple explanation or PERSIST on the Green Building Adviser.I see many problems, not the least of which is that it violates the codes, I haven't bought the CBC version of the iRC (due to take effect January 1st), our current IBC based CBC states: (I would appreciated it if one of you people familiar with the IRC would post the relevant IRC section):
The code goes on to say:
Here is the abstract from ASTM D 226:\ said:1404.2 Water-resistive barrier.
A minimum of one layer of No.15 asphalt felt, complying with ASTM D 226 for Type 1 felt or other approved materials, shall be attached to the studs or sheathing, with flashing as described in Section 1405.3, in such a manner as to provide a continuous water-resistive barrierbehind the exterior wall veneer.
Note that our former UBC also stated "or an approved Kraft paper", that has been deleted in the iBC based code. But also note that the code goes on to say in reference to stucco:\ said:Abstract
This specification covers asphalt-saturated organic felt used in roofing and waterproofing. Two types of asphalt-saturated felts are presented: type I - commonly called No. 15 asphalt felt, and type II - commonly called No. 30 asphalt felt. In the process of manufacture a single thickness of dry felt shall be saturated with an asphaltic saturant. The methods for the determination of openness of the perforations in saturated felts are presented in detail.
Other problems as I see:\ said:2510.6 Water-resistive barriers.
Water-resistive barriers shall be installed as required in Section 1404.2 and, where applied over wood-based sheathing, shall include a water-resistive vapor-permeable barrier with a performance at least equivalent to two layers of Grade D paper.
Exception:
Where the water-resistive barrier that is appliedover wood-based sheathing has a water resistance equal toor greater than that of 60-minute Grade D paper and is separatedfrom the stucco by an intervening, substantiallynonwater-absorbing layer or drainage space.
- Non-permeable walls can create dryrot problems if moisture enters the wall assembly from the exterior due to a flaw or breach in the covering.
- Non-permeable walls can create dryrot problems if moisture enters the wall assembly from the interior, I've heard that each occupant produces somewhere between 3 and 6 gallons of water per day that escapes through the walls (I know that it seems unbelievable but I've seen it in building science articles several times).
- The exterior insulation in PRESIST structures is one form or another of styrofoam, if H.R. 5820, the Toxic Chemicals Safety Act of 2010, passes the House, the Senate, and is signed into law, the following chemicals will be made illegal, it's my position that installing them in structures now is tantamount to painting with lead paint when we knew lead paint was going to be made illegal, or wrapping ductwork with asbestos when we knew the health problems with asbestos. We here also know the problems our firefighter brethren have with toxic foams, to say nothing of the large portions of this nation subject to insect infestation in all foam products.
‘‘(1) ESTABLISHMENT OF LIST.— ‘‘(A) As of the date of enactment of the Toxic Chemicals Safety Act of 2010, there shall be established a list of chemical substances for which safety standard determinations under this section shall first be made, which shall consist of the following chemical substances: ‘‘(i) Bisphenol A. ‘‘(ii) Formaldehyde. ‘‘(iii) N–Hexane. ‘‘(iv) Hexavalent chromium. ‘‘(v) Methylene chloride.‘‘(vi) Trichloroethylene. ‘‘(vii) Vinyl chloride. ‘‘(viii) The following phthalates:
‘‘(I) Benzylbutyl phthalate. ‘‘(II) Dibutyl phthalate. ‘‘(III) Diethylhexyl phthalate. ‘‘(IV) Di-isodecyl phthalate. ‘‘(V) Di-isononyl phthalate. ‘‘(VI) Di-n-hexyl phthalate. ‘‘(VII) Di-n-octyl phthalate.
‘‘(ix) Perchlorate. ‘‘(x) Tetrachloroethylene. ‘‘(xi) Tris (1,3-dichloro-2-propyl) phosphate. ‘‘(xii) Tris (2-chloroethyl) phosphate. ‘‘(xiii) Tris (2,3-dibromopropyl) phosphate.¹
The code goes on to say:
2603.8 Protection against termites.
In areas where the probability of termite infestation is very heavy in accordance with Figure 2603.8, extruded and expanded polystyrene, polyisocyanurate and other foam plastics shall not be installed on the exterior face or under interior or exterior foundation walls or slab foundations located below grade. The clearance between foam plastics installed above grade and exposed earth shall be at least 6 inches (152 mm).
Exceptions:
1. Buildings where the structural members of walls, floors, ceilings and roofs are entirely of noncombustible materials or preservative-treated wood.2. An approved method of protecting the foam plastic and structure from subterranean termite damage is provided.3. On the interior side of basement walls.
/monthly_2010_08/code_termite..jpg.12abbdfb8e0d3c8017bdcc6a8764166b.jpg¹ http://energycommerce.house.gov/documents/20100722/HR5820.pdfAs one can easily see most of the United States is subject to termite infestation, and even areas not subject to termites can be subject to other "critter" infestation. So my question to inspectors is, why is this system being allowed? Particularly in the New England area, and unbelievably I am even seeing it going in in the hot humid climate of Texas, several installations in Austin. Are inspectors in these areas placing energy efficiency ahead of the code? BTW just so your know, the stock answer coming from the energy efficiency fanatics is Lstiburek;s mantra: "Build it tight and ventilate it right", they are running fan systems, (fans, ERVs, HRVs) 24/7 to continually replace the toxic air they have just sealed in with the toxic substances.