• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Pitching a sidewalk right outside an egress door

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,051
Location
Somewhere Too Hot & Humid
If a door is not part of an accessible route, but use primarily as an emergency exit to the exterior of a building, what is the maximum slope you can have if there is a sidewalk running up to the door? The sidewalk is the landing and sidewalk all in one.
 
1:48 or 50...whatever

1010.1.4 Floor Elevation

Diagram
There shall be a floor or landing on each side of a door. Such floor or landing shall be at the same elevation on each side of the door. Landings shall be level except for exterior landings, which are permitted to have a slope not to exceed 0.25 unit vertical in 12 units horizontal (2-percent slope).
Exceptions:
 
1:48 or 50...whatever

1010.1.4 Floor Elevation

Diagram
There shall be a floor or landing on each side of a door. Such floor or landing shall be at the same elevation on each side of the door. Landings shall be level except for exterior landings, which are permitted to have a slope not to exceed 0.25 unit vertical in 12 units horizontal (2-percent slope).
Exceptions:

There are exceptions to 1010.1.4 that may apply, especially exception #2, depending on occupancy. Some exceptions allow for a 7” height difference, and it does not say it has to be a step, so that height can include some kind of slope steeper than 1:48.
Also note that in ADA 404.2.4.1, the maneuvering clearances are only associated with the approach side of the door, so if it is an exit-only door, there would be no accessible maneuvering clearances on the sidewalk side of the door.
 
There are exceptions to 1010.1.4 that may apply, especially exception #2, depending on occupancy. Some exceptions allow for a 7” height difference, and it does not say it has to be a step, so that height can include some kind of slope steeper than 1:48.
Also note that in ADA 404.2.4.1, the maneuvering clearances are only associated with the approach side of the door, so if it is an exit-only door, there would be no accessible maneuvering clearances on the sidewalk side of the door.
Yes, but....the elevation there are some gimmies for, but slope is a bit different....There is very little exception for slope/ pitch IMO...
 