• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Pitching a sidewalk right outside an egress door

jar546

CBO
Joined
Oct 16, 2009
Messages
13,000
Location
Not where I really want to be
If a door is not part of an accessible route, but use primarily as an emergency exit to the exterior of a building, what is the maximum slope you can have if there is a sidewalk running up to the door? The sidewalk is the landing and sidewalk all in one.
 
1:48 or 50...whatever

1010.1.4 Floor Elevation

Diagram
There shall be a floor or landing on each side of a door. Such floor or landing shall be at the same elevation on each side of the door. Landings shall be level except for exterior landings, which are permitted to have a slope not to exceed 0.25 unit vertical in 12 units horizontal (2-percent slope).
Exceptions:
 
1:48 or 50...whatever

1010.1.4 Floor Elevation

Diagram
There shall be a floor or landing on each side of a door. Such floor or landing shall be at the same elevation on each side of the door. Landings shall be level except for exterior landings, which are permitted to have a slope not to exceed 0.25 unit vertical in 12 units horizontal (2-percent slope).
Exceptions:

There are exceptions to 1010.1.4 that may apply, especially exception #2, depending on occupancy. Some exceptions allow for a 7” height difference, and it does not say it has to be a step, so that height can include some kind of slope steeper than 1:48.
Also note that in ADA 404.2.4.1, the maneuvering clearances are only associated with the approach side of the door, so if it is an exit-only door, there would be no accessible maneuvering clearances on the sidewalk side of the door.
 
There are exceptions to 1010.1.4 that may apply, especially exception #2, depending on occupancy. Some exceptions allow for a 7” height difference, and it does not say it has to be a step, so that height can include some kind of slope steeper than 1:48.
Also note that in ADA 404.2.4.1, the maneuvering clearances are only associated with the approach side of the door, so if it is an exit-only door, there would be no accessible maneuvering clearances on the sidewalk side of the door.
Yes, but....the elevation there are some gimmies for, but slope is a bit different....There is very little exception for slope/ pitch IMO...
 
Back
Top