I am installing a pizza oven (self contained, UL listed) into an existing first floor bar (A-2 occupancy) and am trying to determine if this will trigger the requirements of a Level 2 alteration per the 2015 IEBC. Based on my initial reading, it seems like it will but i wanted to get others' opinions. My concern is what this will trigger for the rest of the building. The building is type V-B, unsprinklered, work area is less than 50%. There is a second floor B occupancy and a basement that is associated with the restaurant. All occupancies are currently unseparated. The second floor exit access stairway is enclosed by non-rated construction from the first floor, there are no openings (aside from all of the gaps in the existing construction). The basement stairway is open to the first floor.
My main concern is that it seems like per IEBC 803.2.1 a 30-minute enclosure will be required around the stairs from the second floor and basement. This is going to be extremely difficult considering the existing configuration and construction.
Another point I am trying to figure out is if a rated shaft is required for the grease duct from the pizza oven through the second floor and roof.
IMC 2015 Section 506.3.11 reads "Duct enclosures shall have a fire resistance rating of not less than that of the assembly penetrated and not less than 1-hour." The Exception to this reads that "a duct enclosure is not required for a grease duct that penetrates only a non-fire-resistance-rated roof/ceiling assembly"
The existing second floor and roof that we are penetrating are not rated. Nothing in the IEBC seems to require that they be rated. So by this it would seem that we don't need a rated shaft. Do folks concur? The duct that I am specifying is UL listed, clearance to combustibles will be maintained.
My main concern is that it seems like per IEBC 803.2.1 a 30-minute enclosure will be required around the stairs from the second floor and basement. This is going to be extremely difficult considering the existing configuration and construction.
Another point I am trying to figure out is if a rated shaft is required for the grease duct from the pizza oven through the second floor and roof.
IMC 2015 Section 506.3.11 reads "Duct enclosures shall have a fire resistance rating of not less than that of the assembly penetrated and not less than 1-hour." The Exception to this reads that "a duct enclosure is not required for a grease duct that penetrates only a non-fire-resistance-rated roof/ceiling assembly"
The existing second floor and roof that we are penetrating are not rated. Nothing in the IEBC seems to require that they be rated. So by this it would seem that we don't need a rated shaft. Do folks concur? The duct that I am specifying is UL listed, clearance to combustibles will be maintained.