Benny Welcome and try this for food for thought to support your position
R403.1.6 Foundation anchorage.
Sill plates and walls supported directly on continuous foundations shall be anchored to the foundation in accordance with this section.
This would include the foundation/stem walls
Wood sole plates at all exterior walls on monolithic slabs, wood sole plates of braced wall panels at building interiors on monolithic slabs and all wood sill plates shall be anchored to the foundation with anchor bolts spaced a maximum of 6 feet (1829 mm) on center. Bolts shall be at least 1/2 inch (12.7 mm) in diameter and shall extend a minimum of 7 inches (178 mm) into concrete or grouted cells of concrete masonry units. A nut and washer shall be tightened on each anchor bolt. There shall be a minimum of two bolts per plate section with one bolt located not more than 12 inches (305 mm) or less than seven bolt diameters from each end of the plate section. Interior bearing wall sole plates on monolithic slab foundation that are not part of a braced wall panel shall be positively anchored with approved fasteners. Sill plates and sole plates shall be protected against decay and termites where required by Sections R317 and R318. Cold-formed steel framing systems shall be fastened to wood sill plates or anchored directly to the foundation as required in Section R505.3.1 or R603.3.1.
Exceptions:
1. Foundation anchorage, spaced as required to provide equivalent anchorage to 1/2-inch-diameter (12.7 mm) anchor bolts.
This would allow rebar in lieu of an anchor bolt to provide a positive connection between the foundation and the footer. Most will say this section is referencing the walls of the home. However how many require backfill on the interior of the foundation walls to reduce displacement in a seimic event or exterior pressures on the foundation wall?