Soap box time.
I occasionally get responses from DPs such as "No one has ever asked for that to be on the prints before" or "Why do you need that information on the drawings". I try to clarify as much as possible during plan review so that there are less problems during the construction and inspection process. I cannot assume that the contractors know all of the code requirements.
Whenever I try to "dumb down" the plan review process because we get resistance from the DP's for having to make changes and complaints from the contractors for holding up the job, it always seems to end up causing problems in the end anyway. It always seems like a no win situation no matter which way you go. The DP did not think it was necessary to put it on the drawings and now that it is not, the contractor's excuse for not doing it was that "it was not on the drawings, how was I suppose to know?"
Now for some examples:
Electrical drawings were crude and basic for a psychologist's office that was converted from a SFR. The drawings showed some receptacle, light, emergency lights, switches, etc and said the installation was to be installed to "code". Since it was a relatively easy gut and rewire, I figured any competent electrician would do it right. I figured the inspections would be good enough on the fly. Surprise to me when I got there for the rough wire and found the entire job wired in NM cable including all exposed runs in the basement, attic and above drop ceilings. The outcome was not pretty as you could imagine. I should have held my ground and required more specific information on the prints.
Not showing the vertical grab bar on the drawings is another one. If you don't show it then how does the contractor know he has to install it and will they know enough to add the blocking? This has happened more than once.
Not showing tactile exit signs on the drawings. Sorry, I need to see them because I am tired of failing for this at finals. Yeah, we need that kind of detail
Not providing a list of special inspections. We need that list so that we know what paperwork to expect. How hard can that be to provide that list? If none are required then please state so ON THE DRAWINGS.
Why fight me because I am asking for details on a scupper? There are specs for this in the IPC you know. Already had this issue where they were too small after the EDPM was in place. Not a good time to find out.
How about that load calculation for the electrical service that you are specifying? I like your detailed panel schedule but there is an actual method for load calc. Guess what? We need that too.
I required path of travel, exit access to be shown on the drawings. Most provide this without asking although I have found a few to fudge their numbers when I took a real good look at them. And if you are going to show that, start from inside the offices or inside the apartments not at the door to the office or apartment.
Not specifying what codes and code cycle apply. I need that on the drawings.
We required a door and hardware schedule, a window schedule and a fixture schedule with specs and or model numbers. I just had a submission for illuminated exit signs that did not meet the IECC and was a part number that had been discontinued 3 years ago by Emergi-Lite.
This is just a small example of common items that are often overlooked/not provided.
Thoughts?
Forgive me if I am off base. IMO the BEST building inspectors "share" how they want it done in advance. So I suggest creating a list of "best practices" to insure everyone is on the same page.
Pilots use "knee boards" a checklist for each task. We used to call them FAQ's. If you make the lists, make them available. Let any DO's, architects or engineers edit them as "living documents". If you want them to read it, label it "the code requirements failures most commonly causing rework".
For instance, I talked to Ameren UE about having multiple panels connected to the meter instead of sub panels. You could use a modified copy of the list for "electrical, kitchen remodel" and "New pool circuits"... So a list of requirements as follows:
1. Cable from meter must be (I forgot size), two to six node disconnect after meter.
2. up to 6 nodes may be connected to the meter
3. All County residential is 200 amp service
3a can be overcommitted to 230amps
3b so instead of upgrading panel to 200amps and installing subpanel, you may have 100amp main panel, 100amp shop panel and 30 amp AC circuit off the meter
4. New code requirement: surge protector required either on the panel or on the meter.
5. Outlets must use 12guage (2 wire/ w ground yellow) romex, X outlets max
6. lighting may use 14 gauge (2 wire, white) Romex, Y amps of lights max.
7. Phone number of DP or GC for questions not on FAQ.
8. Links to the section of the electrical code
Identify additional stupid you encounter, recommend the DP attach the lists to the plans. And suggest he have the GC have all subs sign off on each one (or he pays for rework, no guilt).
Doing the same thing for each area. I could probably do one for each area in 15 minutes each