I am working on a renovation of an existing (5) story building
original use was B occupancy on each floor.
First floor (street level) will remain B use.
Floors two-five will change from B to R-2.
NFPA13 sprinkler system is present on all floors and will be re-worked for the existing B occupancy and the new R-2 occupancies.
2017 Ohio Building Code.
Chapter 4 section 430.3 applies.
Horizontal assemblies separating "R" & "B" = 1hour (sprinkler) Table 508.4
Horizontal assemblies separating dwelling units and sleeping units = 1/2 hour with sprinkler [OBC 711.2.4.3 "EXCEPTION"]
My question is related to the existing plaster ceiling of the first floor "B" occupancy.
The plaster ceiling was installed circa 1925 and appears to be about 1-inch thick (lathe to finish coat).
Can i use this plaster ceiling assembly as the 1-hour separation required by Table 508.4?
The plaster ceiling needs to be repaired due to prior modifications to the space over time. The plaster ceiling is suspended from rough sawn wood joist (3x14 @ 12 o.c.) which support a wood floor assembly above).
I didn't see a close approximation in the tables found in OBC 721.
Maybe it's there but i missed it, or misread the table.
How do i confirm the fire rating of the plaster ceiling in question - if one exists?
original use was B occupancy on each floor.
First floor (street level) will remain B use.
Floors two-five will change from B to R-2.
NFPA13 sprinkler system is present on all floors and will be re-worked for the existing B occupancy and the new R-2 occupancies.
2017 Ohio Building Code.
Chapter 4 section 430.3 applies.
Horizontal assemblies separating "R" & "B" = 1hour (sprinkler) Table 508.4
Horizontal assemblies separating dwelling units and sleeping units = 1/2 hour with sprinkler [OBC 711.2.4.3 "EXCEPTION"]
My question is related to the existing plaster ceiling of the first floor "B" occupancy.
The plaster ceiling was installed circa 1925 and appears to be about 1-inch thick (lathe to finish coat).
Can i use this plaster ceiling assembly as the 1-hour separation required by Table 508.4?
The plaster ceiling needs to be repaired due to prior modifications to the space over time. The plaster ceiling is suspended from rough sawn wood joist (3x14 @ 12 o.c.) which support a wood floor assembly above).
I didn't see a close approximation in the tables found in OBC 721.
Maybe it's there but i missed it, or misread the table.
How do i confirm the fire rating of the plaster ceiling in question - if one exists?