Plastic Boxes in Part 3 without CAN/ULC Testing (NBC2015)

Steve French

REGISTERED
Joined
Feb 19, 2025
Messages
14
Location
Nova Scotia, Canada
Hey All,

Looking for a general consensus on the acceptability of plastic boxes being used without firestops where 3.1.9.4. (NBC2015) specifically says anything other than noncombustible boxes installed as per 3.1.9.4.(2) must be firestopped... I've got some Intertek test reports from their lab in China to say that they'll be okay for up to 2-hours in a wall assembly, but the testing standards are all UL - not ULC and not any of the UL standards noted in 1.3.1.2. - and I've refused to accept thus far unless they can give me a test report showing either noncombustible per CAN/ULC-S114 or acceptable performance in a rated wall assembly per CAN/ULC-S101.

Am I in the right here?

Thanks!
- SF
 
Thanks IG. The supplier is fighting hard but they've not come up with anything new, just rehashing the same reports.
They have two and a half options.
1) Show how the outlet boxes are non-combustible; meaning "show us the CAN/ULC S114"
2) Fire stop with putty packs; show us the system."

3) get a fire engineer to submit an alternative solutions.
 
You are correct. This section was updated in the 2020 NBC to clarify that combustible boxes are required to have a firestop system. For clarity, the system has to be FT rated, not just F, which can be challenging.
 
You are correct. This section was updated in the 2020 NBC to clarify that combustible boxes are required to have a firestop system. For clarity, the system has to be FT rated, not just F, which can be challenging.

I'll post the system number once I have it, just in case anyone lands on this thread in the future looking for answers.
 
S115, which again seems odd to me as the box is the penetrant and also the firestop..? I've contact ULC and Intertek Canada to try and speak with someone that knows more about S115 as I can't find a copy to review, but Standards Council of Canada doesn't list Intertek's Shanghai office as an accredited testing service location, which is where the report comes from.

1761655975686.png
 
S115, which again seems odd to me as the box is the penetrant and also the firestop..? I've contact ULC and Intertek Canada to try and speak with someone that knows more about S115 as I can't find a copy to review, but Standards Council of Canada doesn't list Intertek's Shanghai office as an accredited testing service location, which is where the report comes from.

View attachment 16924
Something seems - to use professional terms - hinky AF.

Wanna shoot that whole thing to me in an email?
I'll PM with my addy.
 