Plumbing Fixtures in Demising Wall

ELLEN09US

Member
Joined
Oct 31, 2014
Messages
140
Location
LOS ANGELES
Hello,

Can I have plumbing fixtures in demising wall? I think demising wall should be at least one hour fire rated.
Thank you!
 
"Demising wall" is not a building code term, and is used primarily for real estate purposes in determining areas assigned to tenants of a building. In multi-family residential buildings, there are fire-resistive requirements for "demising walls." However, for other occupancy groups, "demising walls" may or may not be fire-resistance-rated.

If a wall is fire-resistance-rated, it can still have plumbing fixtures. Any penetrations of the wall for piping would need to comply with the requirements for membrane penetrations per Chapter 7 of the IBC.
 
Unless your commercial building is a mall building per Section 402 of the IBC, tenant spaces are not required by the IBC to be separated by fire-resistance-rated assemblies. Local amendments, however, may have been made to require fire-resistance-rated separation walls.
 
Unless your commercial building is a mall building per Section 402 of the IBC, tenant spaces are not required by the IBC to be separated by fire-resistance-rated assemblies. Local amendments, however, may have been made to require fire-resistance-rated separation walls.
Making assumptions on facts not known,
per CBC TABLE 508.4, A-occupancies need separations from M-occupancies
and yes, as Ron has Stated; "...membrane penetrations per Chapter 7 of the IBC. CBC.
 