• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Plumbing Fixtures in Demising Wall

ELLEN09US

Member
Joined
Oct 31, 2014
Messages
140
Location
LOS ANGELES
Hello,

Can I have plumbing fixtures in demising wall? I think demising wall should be at least one hour fire rated.
Thank you!
 
"Demising wall" is not a building code term, and is used primarily for real estate purposes in determining areas assigned to tenants of a building. In multi-family residential buildings, there are fire-resistive requirements for "demising walls." However, for other occupancy groups, "demising walls" may or may not be fire-resistance-rated.

If a wall is fire-resistance-rated, it can still have plumbing fixtures. Any penetrations of the wall for piping would need to comply with the requirements for membrane penetrations per Chapter 7 of the IBC.
 
Unless your commercial building is a mall building per Section 402 of the IBC, tenant spaces are not required by the IBC to be separated by fire-resistance-rated assemblies. Local amendments, however, may have been made to require fire-resistance-rated separation walls.
 
Unless your commercial building is a mall building per Section 402 of the IBC, tenant spaces are not required by the IBC to be separated by fire-resistance-rated assemblies. Local amendments, however, may have been made to require fire-resistance-rated separation walls.
Making assumptions on facts not known,
per CBC TABLE 508.4, A-occupancies need separations from M-occupancies
and yes, as Ron has Stated; "...membrane penetrations per Chapter 7 of the IBC. CBC.
 