Point load on basement slab

A " skeptic" remains among us? Much of what Mark has stated in the past remains true, however in many states picking and choosing your issues remains allowed.
 
The 12" is the punch shear dim. Assume a 45 deg shear plane through the slab (footing) from the edge of the column. So a 4" square column would have a 12" square effective bearing area. That assumes no reinforcment. It gets much more engineery once you start adding reinforcement and your footing becomes a bending plate with spring supports.

I would be ok with a 1500# point load on a 4" slab by inspection.
I just want to weigh in with a thumbs up for use of the term "engineery". gonna have to borrow that one :)
 