1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Polyethylene pipe tubing and fittings (PE)

Discussion in 'Fuel Gas Codes' started by linnrg, Apr 24, 2019.

  1. linnrg

    linnrg Sawhorse

    Joined:
    Mar 17, 2015
    Messages:
    402
    Likes Received:
    105
    This material is approved for use for natural gas in both the UPC and the IFGC.

    Are any of you seeing this being installed on the interior gas piping? Are there any requirements to observe or inspect the heat fusion.
     
  2. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,065
    Likes Received:
    412
    I believe GasCo using it to supply homes in the utility but haven't seen it inside. I see CSST yellow and black jacket being used inside.
     
  3. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,902
    Likes Received:
    1,101
    Not my area

    Question

    Does it have to be

    Listed for underground use?


    Listed for above ground use?????!
     
  4. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,765
    Likes Received:
    960
    I thought it was only allowed underground....Steel risers coming up.....Used it for my garage feed
     
  5. linnrg

    linnrg Sawhorse

    Joined:
    Mar 17, 2015
    Messages:
    402
    Likes Received:
    105
    I too have only seen it underground
     
  6. linnrg

    linnrg Sawhorse

    Joined:
    Mar 17, 2015
    Messages:
    402
    Likes Received:
    105
    found it
    UPC 1210.7 "... outdoors, underground only"
    IFGC 404.15.1 "... outdoors underground only."

    I think the guy that told me they were using it indoors back in the midwest must have confused it with coated CSST
     