Polyethylene pipe tubing and fittings (PE)

linnrg

Sawhorse
Joined
Mar 17, 2015
Messages
516
Location
Sterling Alaska
This material is approved for use for natural gas in both the UPC and the IFGC.

Are any of you seeing this being installed on the interior gas piping? Are there any requirements to observe or inspect the heat fusion.
 
I believe GasCo using it to supply homes in the utility but haven't seen it inside. I see CSST yellow and black jacket being used inside.
 
Not my area

Question

Does it have to be

Listed for underground use?


Listed for above ground use?????!
 
found it
UPC 1210.7 "... outdoors, underground only"
IFGC 404.15.1 "... outdoors underground only."

I think the guy that told me they were using it indoors back in the midwest must have confused it with coated CSST
 
This where it enters the garage:

49479652871_3121bd7f0e_b.jpg

Here it is running across ceiling joist on it's way to the house:

49479873547_205ae64a45_b.jpg

And here we are at the kitchen:

49479172323_9831a42c56_b.jpg

There's nail plates over the iron pipe but not the polyethylene.
 