Positive latching corridor doors in education facility

murdawg67

Member
Joined
Feb 19, 2013
Messages
2
Location
Kansas
Can anyone tell me if anywhere in the 2006 IBC there is a requirement for corridor doors (classroom doors) to be positive latching on either sprinkled or unsprinkled building?
 
Thank you.

I found you by doing a search for my question above. I looked through the forum but could only find references to healthcare.

Thank you for the info.
 
ok, it is a health care occupancy???

what type

hospital, dr. office, psych ward, assisted living???

now the type of occupancy makes a difference
 
I checked the 2006 IBC, and Table 1017.1 requires a 1-hour fire partition for the corridor walls in schools without sprinkler systems. Per Table 715.4, a 1-hour fire partition requires a 20-minute fire door assembly. Fire door assemblies (with a few exceptions) require doors to be self-closing and positive-latching. A fully-sprinklered school does not require rated corridors (Table 1017.1) so the doors are not required to be rated or self-closing/positive-latching. Someone correct me if I'm reading that wrong.

Table 715.4 is shown on this blog post: I Dig Hardware / I Hate Hardware » Decoded: Opening Protectives (June 2011)

I wrote this article with regard to classroom door closers, but it gives the NFPA 101 perspective and might be helpful for background info: I Dig Hardware / I Hate Hardware » Decoded: Closers on Classroom Doors (April 2011)
 
Schools often utilize lockdown plans, such as described in IFC 404.3.3. If the classroom doors are unable to be locked, then special consideration may need to be given to address security concerns.

In the absence of such advance thought, users may improvise and develop a solution that violates provisions of IBC 1008.1.9 for means of egress door operations; perhaps utilizing door wedges to prevent doors from being opened into the classroom or installing surface bolts after the building has been approved for occupancy.
 