Power line clearance

It looks like National Electrical Code 230.0(A) allows a 120/240 volt service to be 3 ft. from a building.

If the service is along a side with gutters I would recommend making sure the service is at least 8 ft. above the gutter (applying NEC 230.24(A)). People don't always watch where their ladders are going.
 
Are you wanting to know how close the barn's roof can be from the house's electrical service?

See NEC 230.24 (B) for vertical clearances from ground
Se NEC 230.24 (A) for clearances above roofs
 