Prep for fuel island

jar546

CBO
Joined
Oct 16, 2009
Messages
12,723
Location
Not where I really want to be
Initially the engineer spec'd out the RMC to be 18" below the finished grade to and at the pumps. I suppose he forgot the 24" requirement.

Anyway, these guys were bending conduit and placing the raceway seals in single digit temperatures. Here is a look at what they have done so far.

514-2.jpg
 
Re: Prep for fuel island

Jeff did they run RMC @ 24" Below grade all the way to fuel dispensing pump or did they convert to PVC per 514.8 exception.....Just asking.
 
Re: Prep for fuel island

jar546 said:
Initially the engineer spec'd out the RMC to be 18" below the finished grade to and at the pumps. I suppose he forgot the 24" requirement.
The EC didn't catch that?
 
Re: Prep for fuel island

chris kennedy said:
jar546 said:
Initially the engineer spec'd out the RMC to be 18" below the finished grade to and at the pumps. I suppose he forgot the 24" requirement.
The EC didn't catch that?

No, I caught that at plan review. I am sure the EC would have caught it too but since I saw it on the plans..............
 