REGISTERED
2015 IPC
Must industrial floor drains in a food processing plant comply with all the requirements of the IPC? Specifically, must all the trench and floor drains be individually trapped, or can there be one trap to serve all these drains? The process sanitary line is connected to a tank where pumps move the waste into mixing tanks for pre-treatment prior to being sent to the municipal sewer system.
Section 1002 requires a trap for each plumbing fixture.
Each Plumbing fixture shall be separately trapped by a liquid-seal trap, except as otherwise permitted by this code. The vertical distance from the fixture outlet to the trap weir shall not exceed 24 inches and the horizontal distance shall not exceed 30 inches measured from the center line of the fixture outlet to the center line of the inlet of the trap. The height of a clothes washer standpipe above a trap shall conform to Section 802.4. A fixture shall not be double trapped
Exceptions:
1. This section shall not apply to fixtures with integral traps.
2. A combination Plumbing fixture is permitted to be installed on one trap, provided that one compartment is not more than six inches deeper than the other compartment and the waist outlets are not more than 30 inches apart.
3. A grease interceptor intended to serve as a fixture trap in accordance with the manufacturer's installation instructions shall be permitted to serve as the trap for a single fixture or a combination sink of not more than three compartment where the vertical distance from the fixture outlet to the inlet of the interceptor does not exceed 30 inches and the developed length of the waste pipe from the most Upstream fixture outlet to the inlet of the interceptor does not exceed 60 in.
4. For drains in multilevel parking structures that discharge to a building storm sewer shall not be required to be individually trapped. Where floor drains in multilevel parking structures are required to discharge to a combined building sewer system, the floor drains shall not be required to be individually trapped provided that they are connected to a main trap in accordance with Section 1103.1.
Section 105 Approval allows modifications and Alternative methods, so a plan reviewer / inspector may possibly allow one trap for all drains.
105.1 Modifications: Where there are practical difficulties involved in carrying out the provisions of this code, the code official shall have the authority to grant modifications for individual cases, upon application of the owner or owners authorized agent, provided the code official shall first find that special individual reason makes the strict letter of this code impractical and the modification conforms to the intent and purpose of this code and that such modification does not lessen health, life, and fire safety requirements. The details of action granting modifications shall be recorded and entered in the files of the plumbing inspection department.
The owner does not want any water to remain in the drains. I do not know if that is obtainable by the code or not.
Thanks,
Must industrial floor drains in a food processing plant comply with all the requirements of the IPC? Specifically, must all the trench and floor drains be individually trapped, or can there be one trap to serve all these drains? The process sanitary line is connected to a tank where pumps move the waste into mixing tanks for pre-treatment prior to being sent to the municipal sewer system.
Section 1002 requires a trap for each plumbing fixture.
Each Plumbing fixture shall be separately trapped by a liquid-seal trap, except as otherwise permitted by this code. The vertical distance from the fixture outlet to the trap weir shall not exceed 24 inches and the horizontal distance shall not exceed 30 inches measured from the center line of the fixture outlet to the center line of the inlet of the trap. The height of a clothes washer standpipe above a trap shall conform to Section 802.4. A fixture shall not be double trapped
Exceptions:
1. This section shall not apply to fixtures with integral traps.
2. A combination Plumbing fixture is permitted to be installed on one trap, provided that one compartment is not more than six inches deeper than the other compartment and the waist outlets are not more than 30 inches apart.
3. A grease interceptor intended to serve as a fixture trap in accordance with the manufacturer's installation instructions shall be permitted to serve as the trap for a single fixture or a combination sink of not more than three compartment where the vertical distance from the fixture outlet to the inlet of the interceptor does not exceed 30 inches and the developed length of the waste pipe from the most Upstream fixture outlet to the inlet of the interceptor does not exceed 60 in.
4. For drains in multilevel parking structures that discharge to a building storm sewer shall not be required to be individually trapped. Where floor drains in multilevel parking structures are required to discharge to a combined building sewer system, the floor drains shall not be required to be individually trapped provided that they are connected to a main trap in accordance with Section 1103.1.
Section 105 Approval allows modifications and Alternative methods, so a plan reviewer / inspector may possibly allow one trap for all drains.
105.1 Modifications: Where there are practical difficulties involved in carrying out the provisions of this code, the code official shall have the authority to grant modifications for individual cases, upon application of the owner or owners authorized agent, provided the code official shall first find that special individual reason makes the strict letter of this code impractical and the modification conforms to the intent and purpose of this code and that such modification does not lessen health, life, and fire safety requirements. The details of action granting modifications shall be recorded and entered in the files of the plumbing inspection department.
The owner does not want any water to remain in the drains. I do not know if that is obtainable by the code or not.
Thanks,