2015 IBC. Proposed deck would be no more than 18" above grade with barrier free access. Deck would abut adjacent structure directly up to the property line with an 1/2" gap. Adjacent structure is two story CMU construction. New deck would treated wood.
Table 601 states that floor construction for Type VB that there is zero (0) hour fire-resistance rated requirements.
Table 602, considering occupancy A, requires 1-h rated construction pretty much in all situations. But table 602 refers to exterior walls. Is this applicable to an uncovered and free-standing deck?
I've also delved in 705.2 per similar projections. Again, this deck isn't an exterior wall assembly.
My concern is that there is no language, that I can locate, that states that this VB construction can be within zero (0) feet of an adjacent structure without any fire separation.
Table 601 states that floor construction for Type VB that there is zero (0) hour fire-resistance rated requirements.
Table 602, considering occupancy A, requires 1-h rated construction pretty much in all situations. But table 602 refers to exterior walls. Is this applicable to an uncovered and free-standing deck?
I've also delved in 705.2 per similar projections. Again, this deck isn't an exterior wall assembly.
My concern is that there is no language, that I can locate, that states that this VB construction can be within zero (0) feet of an adjacent structure without any fire separation.