705.8 would not require the single opening to be protected as it does not exceed the table value, which is the direction I assumed, but the DP has protected some openings and not others, which made me wonder. Because section 602.1 contains the language about openings for t601, I wanted to make sure it wasn't a blanket allowance for t602 like that provided for t601 since both tables are referenced in section 602.1.
To me, the final sentence of 602.1 should identify that the elements being referred to are those found it t601. Seems like this might be better:
"The protection of openings, ducts and air transfer openings in building elements required to be fire resistance rated by t601 shall not be required unless required by other provisions of this code"...or something similar. But, maybe I just think too much, or not enough.