I would be interested to know how other jurisdictions handle the protection of CSST inside walls, especially in exterior walls.
The 2018 IFGC says
I have also heard reports of CSST getting penetrated by pneumatic nail guns when the siding is being installed, but that's just what someone told me.
But, that is not what the contractors around here are used to, so if we start enforcing it this way, we can expect a lot of push-back.
So, in other jurisdictions, do you accept CSST installed to manufacturers specifications as an acceptable alternative that complies with intent? Or do you make them protect the CSST for it's full length? Or some other method?
The 2018 IFGC says
404.7.2 Piping installed in other locations. -Where the piping is located within a framing member and is less than 11/2 inches (38 mm) from the framing member face to which wall, ceiling or floor membranes will be attached, the piping shall be protected by shield plates that cover the width and length of the piping. Where the piping is located outside of a framing member and is located less than 11/2 inches (38 mm) from the nearest edge of the face of the framing member to which the membrane will be attached, the piping shall be protected by shield plates that cover the width and length of the piping.
CSST is to be installed according to the manufacturers instructions and the IFGC according to 404.2. The CSST manufacturers say that if the CSST is not secured in place, it can move out of the way of fasteners and does not need protection in those areas where it is free to move. However, the IFGC makes no exception for the protection of CSST that I can find.I have also heard reports of CSST getting penetrated by pneumatic nail guns when the siding is being installed, but that's just what someone told me.
404.1 Installation of materials. - Materials used shall be installed in strict accordance with the standards under which the materials are accepted and approved. In the absence of such installation procedures, the manufacturer’s instructions shall be followed. Where the requirements of referenced standards or manufacturer’s instructions do not conform to minimum provisions of this code, the provisions of this code shall apply.
So, my reading is that CSST is included in 404.7.2, and would need to be protected for the entire length and width that is within 1 1/2" of the exterior siding or the drywall, it would need to be protected. So, pretty much any time it's installed in a wall, it would need protected from both sides.But, that is not what the contractors around here are used to, so if we start enforcing it this way, we can expect a lot of push-back.
So, in other jurisdictions, do you accept CSST installed to manufacturers specifications as an acceptable alternative that complies with intent? Or do you make them protect the CSST for it's full length? Or some other method?