Dr. J
Silver Member
Background:
2007 NFPA 14 states:
3.3.1 Branch Line. A piping system, generally in a horizontal plane, connecting not more than one hose connection with a standpipe.
3.3.4 Feed Main. The portion of a standpipe system that supplies water to one or more standpipes.
3.3.11 Standpipe. The vertical portion of the system piping that delivers the water supply for hose connections, and sprinklers on combined systems, vertically from floor to floor. The term standpipe can also refer to the horizontal portion of the system piping that delivers the water supply for two or more hose connections, and sprinklers on combined systems, on a single level.
6.1.2 Protection of Aboveground Piping.
6.1.2.1* Standpipe system piping shall be protected from mechanical damage.
6.1.2.2 Standpipes and lateral piping supplied by standpipes shall be located in enclosed exit stairways or shall be protected by a degree of fire resistance equal to that required for enclosed exit stairways in the building in which they are located.
6.1.2.2.1 In buildings equipped with an approved automatic sprinkler system, lateral piping to 2½ in. (65 mm) hose connections shall not be required to be protected.
6.1.2.2.2 Piping connecting standpipes to 1½ in. (40 mm) hose connections shall not be required to be protected.
6.1.2.2.3 Where exit stairways are not required to be enclosed in fire-rated construction, standpipe systems shall be permitted to be installed without the fire resistance required by 6.1.2.2.
2010 NFPA 14 states:
3.3.1 Branch Line. A piping system, generally in a horizontal plane, connecting not more than one hose connection with a standpipe.
3.3.4 Feed Main. The portion of a standpipe system that supplies water to one or more standpipes.
3.3.11 Standpipe. The system piping that delivers the water supply for hose connections, and for sprinklers on combined systems, vertically from floor to floor.
3.3.11.1 Horizontal Standpipe. The horizontal portion of the system piping that delivers the water supply for two or more hose connections, and for sprinklers on combined systems, on a single level.
6.1.2 Protection of Aboveground Piping.
6.1.2.1* Standpipe system piping shall be protected from mechanical damage.
6.1.2.2 Feed Mains, standpipes, horizontal standpipes, and branch piping supplied by standpipes shall be located in enclosed exit stairways or shall be protected by a degree of fire resistance equal to that required for enclosed exit stairways in the building in which they are located.
6.1.2.2.1 In buildings equipped with an approved automatic sprinkler system, feed mains and branch lines supplying 2½ in. (65 mm) hose connections shall not be required to be protected.
For a building requiring standpipes that has Horizontal Exits, there will be horizontal piping to 2½” hose valves on each side of the wall adjacent to each exit opening of horizontal exits.
Questions:
Do you agree with me that there is a significant change between 2007 and 2010? It is my opinion that under 2007, this horizontal piping to the hose valves would be considered “lateral piping to 2½ in. (65 mm) hose connections” and therefore is not required to be protected. However under 2010, 6.1.2.2 clearly states 4 classes of piping that need protection, and 6.1.2.2.1 clearly excludes two of these in sprinklered buildings. The two classes not excluded are “standpipes” and “horizontal standpipes” With the new definition of a “horizontal standpipe” it is clear the piping serving the hose valves at the horizontal exit is required to be protected.
The contrary opinion is that 2007 always required this piping to be protected since the definition of a "standpipe" includes piping “that delivers the water supply for two or more hose connections” , and “standpipes” are not included in 6.1.2.2.1 as piping not needing protection. However, the code says a lot by what it does not say. If they meant that horizontal piping serving only a single hose valve does not need protection they would have said “branch line”, which is clearly defined as serving only a single hose valve outlet, and not “lateral piping to 2½ in. (65 mm) hose connections”. They could also have said “lateral piping to a single 2½ in connection”, but they didn’t. Also, note the "s" on the end of "connections" - obviously plural.
Next. Given the requirement for protection in 2010 (and maybe 2007), what is an acceptable means of protection? There is no NRTL test specified to determine the fire resistive rating. Gypbd enclosure I assume is ok. But how about the various wrap systems? Would you accept the same wrap as used for grease duct? How about this stuff: http://multimedia.3m.com/mws/mediawebserver?mwsId=66666UuZjcFSLXTt4XTtNXT6EVuQEcuZgVs6EVs6E666666--&fn=3M_InteramE-5A-4_PDS_4381-3.pdf ? It is specifically listed for protection of electrical feeders and cable, such as for a fire pump feeder.
2007 NFPA 14 states:
3.3.1 Branch Line. A piping system, generally in a horizontal plane, connecting not more than one hose connection with a standpipe.
3.3.4 Feed Main. The portion of a standpipe system that supplies water to one or more standpipes.
3.3.11 Standpipe. The vertical portion of the system piping that delivers the water supply for hose connections, and sprinklers on combined systems, vertically from floor to floor. The term standpipe can also refer to the horizontal portion of the system piping that delivers the water supply for two or more hose connections, and sprinklers on combined systems, on a single level.
6.1.2 Protection of Aboveground Piping.
6.1.2.1* Standpipe system piping shall be protected from mechanical damage.
6.1.2.2 Standpipes and lateral piping supplied by standpipes shall be located in enclosed exit stairways or shall be protected by a degree of fire resistance equal to that required for enclosed exit stairways in the building in which they are located.
6.1.2.2.1 In buildings equipped with an approved automatic sprinkler system, lateral piping to 2½ in. (65 mm) hose connections shall not be required to be protected.
6.1.2.2.2 Piping connecting standpipes to 1½ in. (40 mm) hose connections shall not be required to be protected.
6.1.2.2.3 Where exit stairways are not required to be enclosed in fire-rated construction, standpipe systems shall be permitted to be installed without the fire resistance required by 6.1.2.2.
2010 NFPA 14 states:
3.3.1 Branch Line. A piping system, generally in a horizontal plane, connecting not more than one hose connection with a standpipe.
3.3.4 Feed Main. The portion of a standpipe system that supplies water to one or more standpipes.
3.3.11 Standpipe. The system piping that delivers the water supply for hose connections, and for sprinklers on combined systems, vertically from floor to floor.
3.3.11.1 Horizontal Standpipe. The horizontal portion of the system piping that delivers the water supply for two or more hose connections, and for sprinklers on combined systems, on a single level.
6.1.2 Protection of Aboveground Piping.
6.1.2.1* Standpipe system piping shall be protected from mechanical damage.
6.1.2.2 Feed Mains, standpipes, horizontal standpipes, and branch piping supplied by standpipes shall be located in enclosed exit stairways or shall be protected by a degree of fire resistance equal to that required for enclosed exit stairways in the building in which they are located.
6.1.2.2.1 In buildings equipped with an approved automatic sprinkler system, feed mains and branch lines supplying 2½ in. (65 mm) hose connections shall not be required to be protected.
For a building requiring standpipes that has Horizontal Exits, there will be horizontal piping to 2½” hose valves on each side of the wall adjacent to each exit opening of horizontal exits.
Questions:
Do you agree with me that there is a significant change between 2007 and 2010? It is my opinion that under 2007, this horizontal piping to the hose valves would be considered “lateral piping to 2½ in. (65 mm) hose connections” and therefore is not required to be protected. However under 2010, 6.1.2.2 clearly states 4 classes of piping that need protection, and 6.1.2.2.1 clearly excludes two of these in sprinklered buildings. The two classes not excluded are “standpipes” and “horizontal standpipes” With the new definition of a “horizontal standpipe” it is clear the piping serving the hose valves at the horizontal exit is required to be protected.
The contrary opinion is that 2007 always required this piping to be protected since the definition of a "standpipe" includes piping “that delivers the water supply for two or more hose connections” , and “standpipes” are not included in 6.1.2.2.1 as piping not needing protection. However, the code says a lot by what it does not say. If they meant that horizontal piping serving only a single hose valve does not need protection they would have said “branch line”, which is clearly defined as serving only a single hose valve outlet, and not “lateral piping to 2½ in. (65 mm) hose connections”. They could also have said “lateral piping to a single 2½ in connection”, but they didn’t. Also, note the "s" on the end of "connections" - obviously plural.
Next. Given the requirement for protection in 2010 (and maybe 2007), what is an acceptable means of protection? There is no NRTL test specified to determine the fire resistive rating. Gypbd enclosure I assume is ok. But how about the various wrap systems? Would you accept the same wrap as used for grease duct? How about this stuff: http://multimedia.3m.com/mws/mediawebserver?mwsId=66666UuZjcFSLXTt4XTtNXT6EVuQEcuZgVs6EVs6E666666--&fn=3M_InteramE-5A-4_PDS_4381-3.pdf ? It is specifically listed for protection of electrical feeders and cable, such as for a fire pump feeder.