2 storey office building with an exit through the lobby. There are both a service room and storage rooms within the same floor area, but down a hallway and around a corner.
9.9.8.5 (3) states that service and storage rooms shall not open directly onto a lobby.
Do you think that:
1) This means that any storage or service room within the same floor area must be separated from the lobby by a fire separation or fire rated door, or
2) The literal interpretation that the doors of the service or storage rooms may not open onto the lobby is correct.
It seems clear to me that 1) is correct, but I have an architect arguing for 2).
Thoughts?