I am trying to layout my PV solar array canopy over an existing parking lot of 750 parking spaces and would like canopy length to exceed 150'. This topic has been discussed several times on this forum and canopies with photovoltaic arrays are best classified as occupancy use U, carports. Section 503.1 from code is below and has a special exception that if I meet certain dimension requirements the canopy does not add to the building height or floor area. How does this apply to at grade parking? I am occupancy U with Type I construction, so my building size is unlimited, and height is also not an issue (5 stories). Are these dimensional requirements only for open/closed parking garages, occupancy type S? Fig. 5-1 looks an awful lot like a surface lot. Can I just run my 40-foot-wide canopy for 200 feet? What am I missing? What do I gain or why am I required to follow these design criteria?
503.1 General.
Unless otherwise specifically modified in Chapter 4 and this chapter, building height, number of stories and building area shall not exceed the limits specified in Sections 504 and 506 based on the type of construction as determined by Section 602 and the occupancies as determined by Section 302 except as modified hereafter. Building height, number of stories and building area provisions shall be applied independently. For the purposes of determining area limitations and type of construction, each portion of a building separated by one or more firewalls complying with Section 706 shall be considered a separate building.
Exceptions:
3. Other than structural requirements, solar photovoltaic panels supported by a structure over parking stalls shall not constitute additional story or additional floor area and may exceed the height limit as specified in exception 2 (above) when the following conditions are met (see Figure 5-1):
503.1 General.
Unless otherwise specifically modified in Chapter 4 and this chapter, building height, number of stories and building area shall not exceed the limits specified in Sections 504 and 506 based on the type of construction as determined by Section 602 and the occupancies as determined by Section 302 except as modified hereafter. Building height, number of stories and building area provisions shall be applied independently. For the purposes of determining area limitations and type of construction, each portion of a building separated by one or more firewalls complying with Section 706 shall be considered a separate building.
Exceptions:
3. Other than structural requirements, solar photovoltaic panels supported by a structure over parking stalls shall not constitute additional story or additional floor area and may exceed the height limit as specified in exception 2 (above) when the following conditions are met (see Figure 5-1):
- The area within the perimeter of the solar photovoltaic array has a maximum rectangular dimension of 40 feet by 150 feet.
- The distance between solar photovoltaic array structures is a minimum of 10 feet clear.
- The driveway aisle separating solar photovoltaic array structures has a minimum of 25 feet clear.
- Solar photovoltaic array structure is used only for parking purposes with no storage.
- Completely open on all sides (other than necessary structural supports) with no interior partitions.