PVC DWV Install phot
Just something to look at and comment about:
I'll start with a few comments:
[1] Air testing of pvc pipe is a "no no!"
[2] What, ...they couldn't put the piping ' inside ' the stud cavities?
[3] Those clean outs are going to be a problem for whoever opens
them up for augering.
[4] The piping is not fastened in place. ...anywhere!
1) It was water tested and he attached the gauge at the bottom to see what the pressure was with 10' of head
2) Superior walls, concrete webs
3) I agree completely
4) I agree completely
Francis - the pressure is 10' of head! (which equals 4.33 psig) But somehow I detect enough sarcasm in your question to indicate that you knew that!
jar - how could the pressure be anything other than 10' of head (=4.33 psig) when there is 10' of head on the system? Static head is dependent only upon the height of the water column in this case.
Going in reverse.... it would take 2.31 vertical feet of pipe to have 1 pound of pressure. So as VP stated 1 foot vertical equals roughly 4.33 psig. That is why the code allows 5 pounds of air pressure on a test in lieu of 10 feet of head pressure.
Love those superior walls!! Any plumber that use's the j hooks is getting out of the gate on the right foot. No idea why the 2 vertical dead ends. Strap all piping per table and all is good.
I’m not good with math as I used to be and as I should be. Normally I would see a single head of water, this photo shows at least 3 verticals over 10’ tied together, I wonder if lets say there are two joined stacks filled to 10’, does this give the same pressure as a single 20’ of head?
Vegas Paul, I appreciate the constructive criticism of how I ask the question, it is just as important as knowing what to ask. Something I need to improve on.
Two joined stacks at 10' yield the same pressure as one single 10' stack... regardless of diameter or # of stacks, the height is the only important factor for static head.
Mule stated:
I will have to respectfully take issue with you on this. Section 312.1 does not allow air to be
used on plastic ( pvc ) piping.
2006 IPC - Section 312.1 & 2006 IRC - P2506.3: " ...All plumbing system piping shall
be tested with either water or, for piping systems other than plastic, by air."
north star said:
>Mule stated:
I see the section where it is not allowed in the 2006 IPC but I don't have a section P2506.3 in my 2006 IRC nor do I find where air is not allowed on PVC.
Do you mean P2503.6? If you are then that section is refering to Water Supply System not the DWV.
So in this situation, since this is posted in the Commercial Plumbing section I would say you are correct. However if this were to be a residential application I need help as to where you can't perform an air test on DWV for residential.
Have I overlooked this in the code?
2006 IRC Looks like air testing is allowed under the IRC
P2503.5.1 Rough plumbing.
DWV systems shall be tested on completion of the rough piping installation by water or air with no evidence of leakage. Either test shall be applied to the drainage system in its entirety or in sections after rough piping has been installed, as follows:
1. Water test. Each section shall be filled with water to a point not less than 10 feet (3048 mm) above the highest fitting connection in that section, or to the highest point in the completed system. Water shall be held in the section under test for a period of 15 minutes. The system shall prove leak free by visual inspection.
2. Air test. The portion under test shall be maintained at a gauge pressure of 5 pounds per square inch (psi) (34 kPa) or 10 inches of mercury column (34 kPa). This pressure shall be held without introduction of additional air for a period of 15 minutes.
Mule & mtlogcabin,
Ooooops, ...my mistake! :eek: You are correct, it should have been Section
P2503.5.1 in the `06 IRC. I should not have cited that code section,
especially since this topic is in the ' Commercial Plumbing ' Thread, and it is
an incorrect [ code ] interpretation on my part.
Do you have any input as to why the Commerical side is more restrictive in
this area, than the Residential is? Seems like a conflict to me, to allow
"testing-by-air" in the Residential applications and NOT in the Commercial.
Your thoughts!
FWIW, I have requested some input / clarification from a pvc pipe manufacturer
on this topic.
I will post the information on here when I receive it.
If he only added the gauge to see what the head pressure is, then what is the black hose for?
Well I did make it sound like air was allowed in commercial testing.......my bad!
Sorry for the delay in getting back with some information.
I e-mailed two pvc pipe manufacturers asking for input on their
products. They were Charlotte Pipe Co. and JM Eagle Co.
While both representatives did say that their companies warn against
the effects of pressure testing pvc pipe with air, apparently they DO
allow it, but in low pressure amounts only. Typically, ...somewhere
below the 9 psi amount.
From Charlotte Pipe Co.
"Charlotte Pipe and Foundry Company recommends testing a DWV
system at 10 feet of hydrostatic pressure (4.3 pounds per square
inch.)........ASTM D 1785 has two notes regarding compresses air or
gases......Note 1. - Pressurizes compressed air or other
compressed gases contain large amounts of stored energy which
present serious safety hazards should a system fail for any reason.
Note 2. - This standard specifies dimensional, performance and
test requirements for plumbing and fluid handling applications,
but does not address venting of combustion gases......You can
compress the molecules in air, but you cannot compress the
molecules in water.......We have a warning stating testing with
compressed air or gases in PVC/ABS/CPVC pipe or fittings
can result in explosive failures and cause severe injury or death.
The 2006 International Plumbing Code, as well as, the 2009
latest edition, Section 312.1 Required Tests......All plumbing
system piping shall be tested with either water or, for piping
systems other than plastic, by air..........Some people confuse
Section 312.2 Drainage and vent air test as an allowable test
for plastic piping.......This is not correct!........Section 312.1 is
very plain that all plumbing systems are to be tested with
water or for piping systems other than plastic, by air."
From JM Eagle:
"JM position in this case is wherever the code and local
jurisdiction allows for air test we recommend for low pressure
air test of DWV PVC pipe".
If anyone wants a copy of the Acrobat files sent from JM
Eagle, send me a PM and I will forward them to you.