I have some lab spaces using plenum style return systems, does this mean I need to fire wrap any existing PVC piping above the ceiling in those areas? I don't see anything in IMC that stipulates this.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
It is more than just plastic piping that comes into play when you have a plenum space. I would review all of 602.2.12018 IMC
602.2.1.7 Plastic plumbing piping and tubing.
Plastic piping and tubing used in plumbing systems shall be listed and labeled as having a flame spread index not greater than 25 and a smoke-developed index not greater than 50 when tested in accordance with ASTM E84 or UL 723.
Exception: Plastic water distribution piping and tubing listed and labeled in accordance with UL 2846 as having a peak optical density not greater than 0.50, an average optical density not greater than 0.15, and a flame spread distance not greater than 5 feet (1524 mm), and installed in accordance with its listing.
Be careful what you use to wrap the pipes withdoes this mean I need to fire wrap any existing PVC piping above the ceiling in those areas?