I have encouraged a few electricians to just encase the acorn in concrete in the wall somehow, maybe in a coffee can or water bottle or something. It would be legal and inexpensive, but really I just wanted the awesome picture. No takers so far...
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I can't see through drywall.Drywall requires a permit and that is when it needs to be caught....
Exactly...the violation is installed with the drywall...not before...I can't see through drywall.
The contrapositive of that is if the GEC to electrode connection is inaccessible, it's required to be non-reversible. Which is what 250.68(A) Exception 2 states, which I had not been aware of. Thanks for the pointer.
But yes, a not accessible, not buried, and reversible connection between the GEC and electrode is not allowed.
Steveray, regarding WH disconnect: I agree with your post and that is how I would approach it. Currently open studs with an electrical panel visual. If drywall is applied and the visual is lost, at that point a WH disco would be required. I noticed a breaker lock which was a surprise to me, someone gave the sparky a heads up on the requirement, presumably the GC.Exactly...the violation is installed with the drywall...not before...
IMO, the acorn ground wire connection to the UFER upright (rebar attached to the footing steel) above the foundation wall would negate the exception No. 1 of NEC 250.68 (A) Accessibility rule. The grounding connection in question is covered with 5/8-inch Type-x drywall used as a ceiling fire separation between the garage and bedrooms above. So to gain access to the connection there would need to be a fire rated access door or panel.That connection is required to be accessible per NEC 250.68(A). So if it covered with drywall, an access panel should be provided at that time.
Certainly if the connection is not buried or encased in concrete, Exception No. 1 does not apply.IMO, the acorn ground wire connection to the UFER upright (rebar attached to the footing steel) above the foundation wall would negate the exception No. 1 of NEC 250.68 (A) Accessibility rule.
I'm a bit unclear on the code path for this conclusion for the IRC.The grounding connection in question is covered with 5/8-inch Type-x drywall used as a ceiling fire separation between the garage and bedrooms above. So to gain access to the connection there would need to be a fire rated access door or panel.