Q: Does this ground wire have to be identified as green?

jar546

CBO
Joined
Oct 16, 2009
Messages
13,000
Location
Not where I really want to be
You are looking at the transformer frame and XO to ground connection. This is a 277/480-120/208 3ph customer owned 225 Kva pad mounted transformer that is fed from a separate service. It is located outside on a concrete pad where it serves a large MDP in the same fenced in area. Since this is not inside a building it does not connect to building steel but instead connects to earth and the structural steel of the pad and fencing that encloses it.
With all of that being said, was the electrician required to mark this ground with green tape?
 

Attachments

  • IMG_5341.JPG
    IMG_5341.JPG
    2.2 MB · Views: 16
I'm not quite sure I understand what you mean. We are talking about grounding only at this point. Could you please clarify?

The use of color is to identify what it is, no? A safety requirement?
if every exposed conduit is the same color then how is one to differentiate exposed ground from, hot or neutral if all wires are in smooth conduit?
 
The use of color is to identify what it is, no? A safety requirement?
if every exposed conduit is the same color then how is one to differentiate exposed ground from, hot or neutral if all wires are in smooth conduit?

The photo does not show any conduit, just the wire coming out of the transformer and going to ground. During inspection, it is obvious what this wire is because everything is open and we can see all connections. You would or should I say shouldn't see any wires that go to a transformer other than POCO transformers. All ungrounded and grounded conductors entering and leaving a transformer will be concealed in conduit and not be seen from the outside.
 
GEC, EGC....whatever....lol....Wasn't thinking on that one...Is it technically a violation if there is no EGC at that point?

I had a guy that did a AL to Cu termination repair job at some condos and he did all of the EGC's in black....That's what I was thinking of....
 
Looks like a trip hazard to me, probably needs a sign at 100 yards saying "Caution, Trip Hazard Ahead!" or "Vorsicht!"
or a couple of bollards painted bright yellow.:p

Most of the grounding I have seen on a generator install has the GE with rod inside the generator door area, ground rod is usually on the plans when pouring the slab.
 