I've got a situation where we're trying to get a SFH built above a parking area. The SFH is ~1650 sq ft, same for the parking area below it at ground level. One side of the garage/SFH combo is proposed to face an ADU also on the property [3.5' gap from assumed property line between the two], and on that side both the ADU and the SFH will have at least 1-hour fire exterior fire rated walls. Two other sides will face an existing property line at ~8' minimum spacing. The other side will face the street and is 15' back. The SFH will be designated a group R-3. The 1st story will be built from non-combustibles (8" thick solid concrete walls, concrete ceiling/2nd story floor)
From CBC Table 705.8 [https://codes.iccsafe.org/s/CABC202...-protection-features/CABC2022P1-Ch07-Sec705.8], it states that for FSD of >5 ft and <10 ft, "
We wanted to have some of the walls be open in the 1st floor parking garage (i.e., no door, no window, just open air). The questions are:
a) Is an "unprotected" opening defined as something with a non-fire rated window or door -- or can it just be an open space in the wall?
b) If it has >50% open area per definition above, will it still meet requirements based on the the proposed fire separation distance?
c) I saw the private parking garage exemption (note j:
but reading up on "https://codes.iccsafe.org/s/CABC2022P1/chapter-4-special-detailed-requirements-based-on-occupancy-and-use/CABC2022P1-Ch04-Sec406.3#:~:text=Private garages and carports shall be classified as Group U,93 m2) in area." states that it is limited to 1000 sq ft of area (but then has a note saying "Exception: The area of a private garage accessory to Group R-3 one- or two-family dwellings shall not be greater than 3,000 square feet in area." -- if the garage is all by itself on the 1st floor, is it "accessory" to? Or does this not matter, since it meets the setbacks per subnote "f"?
From CBC Table 705.8 [https://codes.iccsafe.org/s/CABC202...-protection-features/CABC2022P1-Ch07-Sec705.8], it states that for FSD of >5 ft and <10 ft, "
- f. The area of unprotected and protected openings shall not be limited for Group R-3 occupancies, with a fire separation distance of 5 feet or greater.
We wanted to have some of the walls be open in the 1st floor parking garage (i.e., no door, no window, just open air). The questions are:
a) Is an "unprotected" opening defined as something with a non-fire rated window or door -- or can it just be an open space in the wall?
b) If it has >50% open area per definition above, will it still meet requirements based on the the proposed fire separation distance?
c) I saw the private parking garage exemption (note j:
- "j. The area of openings in a building containing only a Group U occupancy private garage or carport with a fire separation distance of 5 feet or greater shall not be limited.",
but reading up on "https://codes.iccsafe.org/s/CABC2022P1/chapter-4-special-detailed-requirements-based-on-occupancy-and-use/CABC2022P1-Ch04-Sec406.3#:~:text=Private garages and carports shall be classified as Group U,93 m2) in area." states that it is limited to 1000 sq ft of area (but then has a note saying "Exception: The area of a private garage accessory to Group R-3 one- or two-family dwellings shall not be greater than 3,000 square feet in area." -- if the garage is all by itself on the 1st floor, is it "accessory" to? Or does this not matter, since it meets the setbacks per subnote "f"?