It doesn't qualify as either a story or occupiable space by code definitions; doesn't resolve getting these people out of danger in case of an emergency (either on the roof or below).. they need to get into exit stairways and out of the building.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
as posted beforemark handler said:imhothe occupancy a-3 can not be above the thrid level (story).
Regardless of the definition of a story
the options as i see it are to change the area sq footage of the deck
or to change the type of construction.
Huh, woulda never guessed...Coug Dad said:Attended an ICC class last week where roof top "assembly" was discussed. The roof does not have an occupancy, although the means of egress has to be sized to accomodate the use. Therefore, a roof top pool deck would be allowed provided proper egress is provided.
More semantics, but yes, who woulda guessed? Seems like a lot of guessing. The 2012 & 2015 editions of the IBC are supposed to clarify this issue. The instructor referred back to the definition of a story in order to determine occupancy. Since a rooftop does not meet the definition (which has been posted many times already in this thread), there is no occupancy. Same reasoning why you don't classify a flat roof as and S or U occupancy if used as such. Anyway, I digress. His point then was to address the use, and design the means of egress accordingly for widths, number of exits, exit access, travel distance, cpt, etc.texasbo said:Huh, woulda never guessed...
The instructor was FOS. [302.1] Structures or portions of structures shall be classified with respect to occupancyPapio Bldg Dept said:More semantics, but yes, who woulda guessed? Seems like a lot of guessing. The 2012 & 2015 editions of the IBC are supposed to clarify this issue. The instructor referred back to the definition of a story in order to determine occupancy. Since a rooftop does not meet the definition (which has been posted many times already in this thread), there is no occupancy. Same reasoning why you don't classify a flat roof as and S or U occupancy if used as such. Anyway, I digress. His point then was to address the use, and design the means of egress accordingly for widths, number of exits, exit access, travel distance, cpt, etc. I believe that is a fair and reasonable opinion about how to handle a 4 Story, roof top being used as an assembly occupancy. In otherwords. No occupanc. Same holds true if you fenced in an 8,000sf open air volleyball court with wood and stucco walls 12 feet high on top of a roof or at ground level. With no area modifications, this would exceed the allowable areas if we assigned it an occupancy classification per table 503. Do we really need to sprinkle the space to get an area increase? Has common sense flown the coop? I can tell you this AHJ would not assign an occupancy classification, whether up on a roof or not. Do you MOE calcs/design per the use/function and move on, in my opinion.
Good points. FOS might be a bit excessive.brudgers said:The instructor was FOS. [302.1] Structures or portions of structures shall be classified with respect to occupancy
Nothing about stories or even buildings.
See Occupancy A5 for a counter example which shows the intent of the code.
When someone says something as utterly stupid as "Occupancy doesn't apply" and then rationalizes it based on an unrelated definition rather than an actual reading of Chapter 3 and 4, they are obviously an idiot. © When they assert such stupidity as an instructor while presenting themselves as an expert and in the role of instructor, then they are FOS.Papio Bldg Dept said:Good points. FOS might be a bit excessive. Following your logic, what occupancy classification to roofs that aren't used for assembly would you assign?
Following the code, it would be (underline, mine):Papio Bldg Dept said:...Following your logic, what occupancy classification to roofs that aren't used for assembly would you assign?
302.1 General. Structures or portions of structures shall be classified with respect to occupancy in one or more of the groups listed below. A room or space that is intended to be occupied at different times for different purposes shall comply with all of the requirements that are applicable to each of the purposes for which the room or space will be occupied. Structures with multiple occupancies or uses shall comply with Section 508. Where a structure is proposed for a purpose that is not specifically provided for in this code, such structure shall be classified in the group that the occupancy most nearly resembles, according to the fire safety and relative hazard involved.
Having re-read the thread, in particular mt's post on special-purpose roofs, proved to be more helpful for me in understanding the intent of the code than anything I have read or heard in the last week on this subject. It tells me that the intent of the code is to assign an occupancy classification to all buildings and structures.mtlogcabin said:Don't forget 1607.11.2.2 Special-purpose roofs.
Roofs used for promenade purposes, roof gardens, assembly purposes or other special purposes, and marquees, shall be designed for a minimum live load, Lo, as specified in Table 1607.1. Such live loads are permitted to be reduced in accordance with Section 1607.9. Live loads of 100 psf (4.79 kN/m2) or more at areas of roofs classified as Group A occupancies shall not be reduced.
Thanks alora. Between you, brudgers and mt, I see an intent in the code that wants to assign an occupancy to the roof as it is part of the building/structure, and other sections are using that occupancy classification to prescribe design standards (I do have some questions about various conditions for MOE to the roof, but I am confident if I re-read the code sections on stairs and roof access I will be able to answer them). I am however, more of the inclination that, as texasbo believes, Table 503, for heights and areas does is not applicable for occupancies of non-stories outside the definitions of the allowable building area. Using logic (however unapplicable, unfounded or inept my use of it may be), tends to lead me towards texasbo's conclusion. When brudgers does not agree with my instructor, from whom I have taken several ICC training classes, my lebenswelt tends to get a little shaky, I start looking at other examples where holding a project to Table 503 limitations would not make sense.alora said:Following the code, it would be (underline, mine):
Maybe, but maybe not. I would be willing to discuss some additional peripheral subjects.Papio Bldg Dept said:Am I to assume we are now just haggling over price?
MT: note that the code uses the term stories, not floors. It doesn't allow assembly more than 3 stories in height, not more than 3 floors. In the case at hand, it is not more than 3 stories.mtlogcabin said:The use on the roof and the height limits based on construction type should determine if the use is permitted.Example a 4 story V-B hotel should not be permitted to have a assembly use on it as the use is more than 3 floors in height. change the construction type and it will work.
Could the same hotel have a heliport on the roof, or a small dining area with less an OL of less than 50?
See section 506.4 Re: The original postPapio Bldg Dept said:Thanks alora. Between you, brudgers and mt, I see an intent in the code that wants to assign an occupancy to the roof as it is part of the building/structure, and other sections are using that occupancy classification to prescribe design standards (I do have some questions about various conditions for MOE to the roof, but I am confident if I re-read the code sections on stairs and roof access I will be able to answer them). I am however, more of the inclination that, as texasbo believes, Table 503, for heights and areas does is not applicable for occupancies of non-stories outside the definitions of the allowable building area. Using logic (however unapplicable, unfounded or inept my use of it may be), tends to lead me towards texasbo's conclusion. When brudgers does not agree with my instructor, from whom I have taken several ICC training classes, my lebenswelt tends to get a little shaky, I start looking at other examples where holding a project to Table 503 limitations would not make sense.
Residential Occupancies have an occupant load of 1/200 sf. See Table 1004.1.1Dawgbark said:No one knows what the occupant load of the building is, what the sq.ft. of the roof top is. What If one person of the condo complex owns the top floor and the roof top which is possible the the occupant load is one.
Yeah, just because you don't comprehend something, it doesn't exist.texasbo said:Maybe, but maybe not. I would be willing to discuss some additional peripheral subjects. It's been established that the roof is not a story, and therefore not subject to height in stories. In terms of area, the code is pretty explicit in its definition, so if you want to stick something on the roof, area has already been taken care of. But let's say the occupied roof exceeded allowable height in feet. Would that be a violation? I would consider discussing it. I do like poo poo humor though, so let's continue this.