R Value Requirement for Cathedral Ceiling

Skyy123

REGISTERED
Joined
Feb 15, 2017
Messages
1
Location
Westchester County NY
Hi Everyone,

Were remodeling a home in Putnam County NY, the previous Sheetrock was mounted directly on 2x10 rafters, we removed all sheetrock (2100 sq ft) I'm trying to interrupt the codes, i believe I can use R30 but it doesn't look like I'm allowed to do this for more the 500sq ft is that correct? My other question is ventilation part of the code? Because there are no working soffits or ridge vents the previous install was a hot roof and everything was sealed. I was told by the guy at Home Depot that I must have ventaltion baffles installed but obviously with the current setup they will do nothing. Any help is greatly appreciated thank you.
 
Closed cell foam (R- 6-6.5) would provide the required R-38 with NO ventilation required.
 