2018 IBC. R2 occupancy. VB. 2-story. Fully sprinkled, nfpa 13
This is basically 8 apartments with on center interior corridor leading to an enclosed stairway on each end of the corridor which then exits to the exterior. Pretty straight forward.
Question is if the stairs would be required to be rated?
1019.3 below would say that the stairs are NOT required to be rated because they are only connecting two stories:
1019.3 Occupancies other than Groups I-2 and I-3.
In other than Group I-2 and I-3 occupancies, floor openings containing exit access stairways or ramps that do not comply with one of the conditions listed in this section shall be enclosed with a shaft enclosure constructed in accordance with Section 713.
1.Exit access stairways and ramps that serve or atmospherically communicate between only two stories. Such interconnected stories shall not be open to other stories.
BUT, per 1020.6 below, and my general intuition, the stairs should have the same rating as the 2nd story corridor (which is 1/2 hr per table 1020.1):
1020.6 Corridor continuity.
Fire-resistance-rated corridors shall be continuous from the point of entry to an exit, and shall not be interrupted by intervening rooms. Where the path of egress travel within a fire-resistance-rated corridor to the exit includes travel along unenclosed exit access stairways or ramps, the fire-resistance rating shall be continuous for the length of the stairway or ramp and for the length of the connecting corridor on the adjacent floor leading to the exit.
I'm really over thinking this - sigh.
This is basically 8 apartments with on center interior corridor leading to an enclosed stairway on each end of the corridor which then exits to the exterior. Pretty straight forward.
Question is if the stairs would be required to be rated?
1019.3 below would say that the stairs are NOT required to be rated because they are only connecting two stories:
1019.3 Occupancies other than Groups I-2 and I-3.
In other than Group I-2 and I-3 occupancies, floor openings containing exit access stairways or ramps that do not comply with one of the conditions listed in this section shall be enclosed with a shaft enclosure constructed in accordance with Section 713.
1.Exit access stairways and ramps that serve or atmospherically communicate between only two stories. Such interconnected stories shall not be open to other stories.
BUT, per 1020.6 below, and my general intuition, the stairs should have the same rating as the 2nd story corridor (which is 1/2 hr per table 1020.1):
1020.6 Corridor continuity.
Fire-resistance-rated corridors shall be continuous from the point of entry to an exit, and shall not be interrupted by intervening rooms. Where the path of egress travel within a fire-resistance-rated corridor to the exit includes travel along unenclosed exit access stairways or ramps, the fire-resistance rating shall be continuous for the length of the stairway or ramp and for the length of the connecting corridor on the adjacent floor leading to the exit.
I'm really over thinking this - sigh.