2018 ISPSC
305.2.5 Closely Spaced Horizontal MembersWhere the barrier is composed of horizontal and vertical members and the distance between the tops of the horizontal members is less than 45 inches (1143 mm), the horizontal members shall be located on the pool or spa side of the fence. Spacing between vertical members shall not exceed 1-3/4 inches (44 mm) in width. Where there are decorative cutouts within vertical members, spacing within the cutouts shall not exceed 1-3/4 inches (44 mm) in width.305.2.6 Widely Spaced Horizontal MembersWhere the barrier is composed of horizontal and vertical members and the distance between the tops of the horizontal members is 45 inches (1143 mm) or more, spacing between vertical members shall not exceed 4 inches (102 mm). Where there are decorative cutouts within vertical members, the interior width of the cutouts shall not exceed 1-3/4 inches (44 mm).I would not allow it, unless the beach area could be argued as being a natural barrier, either per 305.6 or 305.7.
305.6 Natural BarriersIn the case where the pool or spa area abuts the edge of a lake or other natural body of water, public access is not permitted or allowed along the shoreline, and required barriers extend to and beyond the water's edge not less than 18 inches (457 mm), a barrier is not required between the natural body of water shoreline and the pool or spa.305.7 Natural TopographyNatural topography that prevents direct access to the pool or spa area shall include but not be limited to mountains and natural rock formations. A natural barrier approved by the governing body shall be acceptable provided that the degree of protection is not less than the protection afforded by the requirements of Sections 305.2 through 305.5.
But the horizontal bars in the photos would not in your opinion?For the horizontal design to comply as a pool barrier, it would require the posts to be spaced no greater than 1-3/4 inch apart.
Right. Horizontals can be at any spacing, but when they are less than 45 inches apart they cause the maximum spacing of the verticals to be 1-3/4 inch.But the horizontal bars in the photos would not in your opinion?
Since I am in a 175mph zone, exposure D, white resin comes with an entirely different engineering problem.This is a variation from the original post but would you allow white resin six feet in height as a permanent in ground pool barrier? We are under the 2018 IBC. My concern is that I've seen these panels blown out due to high winds so I don't consider them to be sturdy.
That's not your job. Just tell them how to get the code on line. The fence guys always got right for me. The owner get's it right about 50% of the tome for me.In my experience, the pool contractor does not mention the barrier requirement to the owner until they need a final approval. At that point the contractor tells the owner to request an inspection. The contractor convinces the owner that it is the inspector's task to educate the owner on barrier code. Then the inspector is put on the spot to design the barrier. I have had some awful encounters.....some that cost thousands of dollars.....and it's always a surprise for the owner.
To combat this I seek out the owner at the pre-gunite inspection. I provide handouts and make it clear that the contractor is responsible for the barrier. That does not have an effect and I still get stuck with the owner and the fence.
It is dumbfounding when a company that is in the business of fabricating and installing fence and gates gets it wrong. That has happened dozens of times in spite of my best effort.
They call the office manager and complain that I am not helpful. Then I have to explain it to a manager to. Come to think of it, that's the case with a lot of corrections....especially electrical.That's not your job. Just tell them how to get the code on line.
They call the office manager and complain that I am not helpful. Then I have to explain it to a manager. Come to think of it, that's the case with a lot of corrections....especially electrical.
Jar does the FL code have you measure the pool barrier from grade or standing surface/floor on a wood deck?
JAR,There are almost 90 units at this commercial R2 condo. What are your code thoughts on this pool barrier?
Quite often I spent way more time explaining a correction than it took to find the correction.....well not so much lately what with the virtual inspections and all but it used to take up much of my day.If there is one thing that has consistently gotten inspectors thrown out of my jurisdiction due to complaints received by the town manager, it was the unwillingness of the inspector to at least give some guidance and explain the code. You don't have to design it for them but at least explain the code section and what it means, aka your interpretation. We have a third party that assists us with inspections and there has been 4 of their inspectors that were told not to return over the past 2 years.
That is an excellent point but the intent is what is important for safety. I would err on the side of caution and let them go to an appeals board if they did not like it.So do we inspect to the definition of what the code says is "grade" when measuring the barrier on the outside of the pool area or should we assume that the code is wrong and measure from the standing surface? Grade can be under a deck.
[RB] GRADE. The finished ground level adjoining the
building at all exterior walls.
Jar,There are almost 90 units at this commercial R2 condo. What are your code thoughts on this pool barrier?