• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

R2, single stair, 3-story: roof deck & penthouse questions

With an occupant load below 50 it would not be an 'assembly occupancy' as the exceptions to assembly occupancy allow it to be classified as a business occupancy or as part of the occupancy of which it is a part (in this case an R-2).
The codes are actually very clear about the questions at hand.
 
1. 3 story building + mezzanine: Put a roof & perimeter guardrails rails over 50% of that 4th floor deck and call it a mezzanine which does not contribute to either building area or number of stories. This will need to be included/added to fire area and sprinkled.
2. yes, you can install a hatch, req. for any equip. access.
3. You do not count the mezzanine as a story, Design the stairs in compliance with interior exit stairway requirements and eliminate the CPET issue.

...have to keep the occupancy <10 or mezzanine required to be open to floor below.

or just redesign you 3rd floor with a mezzanine and stay off the damn roof!
 