Francis Vineyard
REGISTERED

Figure R404.1.5(1) “FOUNDATION WALL CLAY MASONRY CURTAIN WALL WITH CONCRETE MASONRY PIERS”
The minimum spacing for piers to provide lateral bracing of curtain walls are provided in Table 606.9; this is not the 6 ft. spacing shown in Figure R404.1.5(1)!
“Anchorage shall be in accordance with Section R403.1.6, Figure R404.1.5(1)” This is the 6 ft. spacing requirement for piers with clay masonry.
Section R403.1.6; “Bolts shall be at least ½” in dia. and shall extend a min. of 7” into concrete or grouted cells of concrete masonry units.
So the code allows 4 inch CMU wall and does not specifically prohibiting anchor bolts in these walls?
Definitions:
MASONRY UNIT. Brick, tile, stone, glass block or concrete
block conforming to the requirements specified in Section
2103 of the International Building Code.
Clay. A building unit larger in size than abrick, composed
of burned clay, shale, fire clay or mixtures thereof.
Concrete. A building unit or block larger in size than 12
inches by 4 inches by 4 inches (305 mm by 102 mm by 102
mm) made of cement and suitable aggregates.
Glass. Nonload-bearing masonry composed of glassunits
bonded by mortar.
Hollow. A masonry unit whose netcross-sectional area in
any plane parallel to the loadbearing surface is less than75
percent of its gross cross-sectional area measured in the
same plane.
Solid. A masonry unit whose netcross-sectional area in
every plane parallel to the loadbearing surface is 75 percent
or more of its cross-sectional area measured in the same
plane.