mark handler
try standing on your headbrudgers said:Not enough blood flowing to the brain?
Could you copy and paste that? We have never been on the IRC (will be on the 1st) but I recall the building inspectors talking about that on the old Bulletin Board, as I recall it didn't say "flanged windows were considered self flashing", but as I recall it did reference "self flashing" windows, but again no manufacturer has ever made a "self-flashing window".Robert said:Opps!--I opened up my 2003 IRC and quoted from it where flanged windows were considered self flashing. It was taken out in 2006.
Most foam boards I've seen have a vapor perm higher than plywood or sheet rock. The foil covering will lower the lower perm.KZQuixote said:Hi Robert,Regarding the foam board, I can only hope that it is covered with a WRB and if it is the technique would be the same as if it were over OSB sheathing.
Do you see a lot of exterior foam insulation board? I don't believe that stuff breathes very well.
Regards
Bill
I've seen buildings in hurricane prone regions where the rafters are attached by three toenails...before a hurricane.GHRoberts said:It is difficult to argue that flashing is needed.I have seen houses where despite there being no flashing, there is no weather damage to the structure.
I have seen houses where despite careful flashing there is weather damage to the structure.
Also be aware that they are New England cold climate gurus, foams can't be used anywhere near the ground in most of the United States.2007 CBC said:2603.4.1.10 Siding backer board. Foam plastic insulation of not more than 2,000 British thermal units per square feet (Btu/sq. ft.) (22.7 MJ/m2) as determined by NFPA 259 shall be permitted as a siding backer board with a maximum thickness of 0.5 inch (12.7 rom), provided it is separated from the interior of the building by not less than 2 inches (51 mm) of mineral fiber insulation or equivalent or where applied as insulation with re-siding over existing wall construction.
I guess I posted the map before I posted the IBC prohibition.Sandman said:There is no code prohibition for insulating foam.
Furthermore, Environmentalists are banning the stuff worldwide for clogging up the oceans killing the fish and birds.2007 CBC (IBC) said:2603.8 Protection against termites. In areas where the probability of termite infestation is very heavy in accordance with Figure 2603.8, extruded and expanded polystyrene, polyisocyanurate and other foam plastics shall not be installed on the exterior face or under interior or exterior foundation walls or slab foundations located below grade. The clearance between foam plastics installed above grade and exposed earth shall be at least 6 inches (152 mm).Exceptions:
1. Buildings where the structural members of walls, floors, ceilings and roofs are entirely of noncombustible materials or preservative-treated wood.
2. An approved method of protecting the foam plastic and structure from subterranean termite damage is provided.
3. On the interior side of basement walls.