Keystone
Can someone point me to the section in ACI, think it's 318 or 315, stipulating rebar shall be radius in foundation corners?
If you do not have radius corner bars installed then how do you meet the requirement of a rebar splice to overlap a minimum 20 bar diameters?
The 20 bar overlap and radius is usually specified by the engineer, back when I was a young carpenter we bent the rebar over our knees, once I graduated to architect designed buildings this was always specified and I bought a rebar cutter bender that bent the proper radius. Back when we were bending it over our knees no inspector ever said anything, so I always assumed that the engineers got their radii from the ACI handbook.I had the impression that the 20 bar diameter overlap was for CMU construction only.
I forget the exact numbers but for typical foundation reinforcement I believe you need more like 40 diameters. At corners this issue is addressed by providing hooks which are hooked around a vertical bar.
https://law.resource.org/pub/us/cfr/ibr/001/aci.318.1995.pdfI might have a copy.....
ICE, this extract from 318-11 says in section 7.10.4.5 the laps for spirals should be a minimum of 48d. Hope that helps.Maybe in one of the mansions that conarb built but I haven't encountered that in any residential application. I would like to know what ACI 318 recommends for the lap splice if anyone has a copy. Now that I think about it, I might have a copy.....it would be so much easier if someone could tell me.
In years past I did deal with hooks in a lot of places on large commercial projects. Thankfully, the steel details were supervised by a deputy inspector.
The requirement for minimum laps doesn't apply for corners. I do a good bit of rebar detailing and some engineers specify them, some specify them only for the outside bars and some don't specify them at all. I'm not sure what criteria they use to make that determination but many jobs to not have them at all. I've even had just returned for corrections when I put them in and they were not called out.If you do not have radius corner bars installed then how do you meet the requirement of a rebar splice to overlap a minimum 20 bar diameters?
Yeah, ACI, remember our old buddy Uncle Bob screaming that the IRC was a stand-alone code?I must not be paying attention because I keep seeing Masonry and CMU requirements but nothing for a footing. Is there something out there for a footing?