Just had a customer use sdr 35 for radon prep, tee is buried so I cant see if it gasketed or glued…..And of course he is not there for inspection…..
Here is our CT section 2015 based:
(Add) AF104.2 “T” fitting and vent pipe. Before a slab is cast or other floor system is installed,
a 3-inch “T” fitting shall be inserted beneath the soil-gas-retarder. The “T” fitting shall be
surrounded by aggregate consisting of material that will pass through a 2-inch (51 mm) sieve and
be retained by a .-inch (6.4 mm) sieve not less than an 8-inch deep by 24-inch diameter hole.
The aggregate shall be wrapped in filter fabric or equivalent material. The “T” fitting shall be
connected to a 3-inch-diameter (76 mm) ABS or PVC vent pipe extending from the basement
through the conditioned space of the dwelling and terminate and be capped not less than 12
inches (305 mm) above the roof in a location not less than 10 feet (3048 mm) away from any
window or other opening into the conditioned spaces of the building that is less than 2 feet (610
And here is 2021 IRC:
AF103.6.1 Vent pipe. A minimum 3-inch-diameter (76
mm) ABS, PVC or equivalent gastight pipe shall be
embedded vertically into the subslab aggregate or other
permeable material before the slab is cast. A “T” fitting or
equivalent method shall be used to ensure that the pipe
opening remains within the subslab permeable material.
Obviously he can’t use SDR35 for plumbing in the building, but our code is silent for radon and the 2021 just says “gas tight”….Any thoughts?
Here is our CT section 2015 based:
(Add) AF104.2 “T” fitting and vent pipe. Before a slab is cast or other floor system is installed,
a 3-inch “T” fitting shall be inserted beneath the soil-gas-retarder. The “T” fitting shall be
surrounded by aggregate consisting of material that will pass through a 2-inch (51 mm) sieve and
be retained by a .-inch (6.4 mm) sieve not less than an 8-inch deep by 24-inch diameter hole.
The aggregate shall be wrapped in filter fabric or equivalent material. The “T” fitting shall be
connected to a 3-inch-diameter (76 mm) ABS or PVC vent pipe extending from the basement
through the conditioned space of the dwelling and terminate and be capped not less than 12
inches (305 mm) above the roof in a location not less than 10 feet (3048 mm) away from any
window or other opening into the conditioned spaces of the building that is less than 2 feet (610
And here is 2021 IRC:
AF103.6.1 Vent pipe. A minimum 3-inch-diameter (76
mm) ABS, PVC or equivalent gastight pipe shall be
embedded vertically into the subslab aggregate or other
permeable material before the slab is cast. A “T” fitting or
equivalent method shall be used to ensure that the pipe
opening remains within the subslab permeable material.
Obviously he can’t use SDR35 for plumbing in the building, but our code is silent for radon and the 2021 just says “gas tight”….Any thoughts?