I have a section of ramp that needs to flare out at the top. I don't see anything preventing what I show below. (6" rise, no handrails). Am I correct?

1748980070426.png
 
Where is your project located? More specifically, what are the applicable codes and regulations for your project?

Out here in California, our state modified the model ADA regs into 11B-505.2, which only allows the omission on handrails at <6" high ramps that occur at door landings.
 
Am I correct?
I can’t think of anything to prevent the ramp from changing in width either, just be careful not to reduce a required means of egress width per 1005.4.

You say there isn’t a handrail because it is a 6” rise, keep in mind you’re limited to a 1/2” drop-off before you need edge protection per 1012.10 Point 3.
 
I can’t think of anything to prevent the ramp from changing in width either, just be careful not to reduce a required means of egress width per 1005.4.

You say there isn’t a handrail because it is a 6” rise, keep in mind you’re limited to a 1/2” drop-off before you need edge protection per 1012.10 Point 3.
Thank you. Curbs both sides.
 