• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Range Hood Duct Material

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,022
Location
Somewhere Too Hot & Humid
What a surprise in this high rise condo to find this newly installed duct ready for connection to the new range hood. What is the material?
6289D012-4483-45C3-8D8A-D7EEC644D629.jpeg6086CF4C-05DF-4FAE-B223-9F3C46255BE8.jpeg
 
Last edited:
IRC 1503.4 and IMC 505.3 both require ducts for domestic cooking exhaust equipment to be made of galvanized steel, stainless steel, or copper. IMC also includes a requirement for smooth interior finish. So no, that duct does not meet the requirements for a domestic range hood.
 
You can see the ridgid pipe in the first picture going through the wall. Looks like they only need a couple of elbows ... why such a long piece of flex?
 
California Mechanical code
504.3 Domestic Range. Ducts used for domestic kitchen range or cooktop ventilation shall be of metal and shall have smooth interior surfaces.
Exception: Ducts for domestic kitchen downdraft grill-range ventilation installed under a concrete slab floor shall be per- mitted to be of approved Schedule 40 PVC provided:
(1) The under-floor trench in which the duct is installed shall be completely backfilled with sand or gravel.
(2) Not more than 1 inch (25.4 mm) of 6 inch diameter (152 mm) PVC coupling shall be permitted to protrude above the concrete floor surface.
Exception: Where an exhaust duct power ventila- tor, in accordance with Section 504.4.2.3, is used, the maximum length of the dryer exhaust duct shall be permitted to be in accordance with the dryer exhaust duct power ventilator manufacturer’s instal- lation instructions.
(3) PVC pipe joints shall be solvent cemented to provide an air and greasetight duct.
(4) The duct shall terminate above grade outside the build- ing and shall be equipped with a back-draft damper.
 