Sifu
- Joined
- Sep 3, 2011
- Messages
- 3,390
In high-rise buildings constructed under the 1994 UBC, corridors may be required to be rated even if they are sprinklered per UBC 1005.7. So my question is with the term "within office spaces". Does this mean within a tenant space, or does it include the entire group of separate office spaces on a given floor?
The IBC basically provides an exception for corridors if the building is sprinklered, but the UBC stops short of that by limiting the occupant load to 100, just not sure where the limitation applies.
1994 UBC
1005.7 Construction. Walls of corridors serving a Group R, Division 1 or Group I Occupancy
having an occupant load of 10 or more and walls of corridors serving other occupancies having an
occupant load of 30 or more shall be of not less than one-hour fire-resistive construction and the
ceilings shall not be less than that required for a one-hour fire-resistive floor or roof system.
EXCEPTIONS:
1. One-story buildings housing Group S, Division 2 and Group F, Division 2 Occupancies.
2. Corridors more than 30 feet (9144 mm) in width where occupancies served by suc1 corridors have at
least one exit independent from the corridor. (See Chapter 4 for covered malls.)
3. Exterior sides of exterior exit balconies.
4. In Group I, Division 3 Occupancies such as jails, prisons, reformatories and sim1lar buildings with
open-barred cells forming corridor walls, the corridors and cell doors need not be fire re~ istive.
5. Corridor walls and ceilings need not be of fire-resistive construction within office spaces having an
occupant load of 100 or less when the entire story in which the space is located is equipped with an automatic sprinkler system throughout and an automatic smoke-detection system installed within the corridor. The actuation of any detector shall activate alarms audible in all areas served by the corridor.
6. In other than Type I or II construction, exterior exit balcony roof assemblies may be of heavy-timber
construction without concealed spaces.
7. Within office spaces occupied by a single tenant, partial height partitions which form corridors and
which do not exceed 6 feet (1829 mm) in height need not be fire resistive, provided the) are constructed in
accordance with Section 601.5 and are not more than three fourths of the floor-to-ceiling height.
8. Corridor walls and ceilings need not be of fire-resistive construction within office spaces having an occupant load of 100 or less when the building in which the space is located is equipped with an automatic sprinkler system throughout.
1994 UBC
EXCEPTIONS: