So, I have a townhouse in review at the moment. They want to use U373 for the rated wall. It is a 2 hr rated wall assembly for load bearing. They want to use configuration B which is shown in section as:
1/2" drywall
2x4 studs at 24" o.c.
3/4" air space
(2) 1" drywall liners using friction fitted H shaped studs
3/4" air space
2x4 studs at 24" o.c.
1/2" drywall
Now, to me, this is one common 2 hour rated wall assembly where no plumbing or mechanical duct or equipment can be installed in either inside cavity.
link to UL website for configuration A and B
https://iq.ulprospector.com/en/profile?e=14938
link to Georgia Pacific for only Configuration B
https://www.buildgp.com/assembly/area-separation-wall-2/
Configuration A shown as:
1/2" drywall
2x4 studs at 24" o.c.
3/4" air space
(2) 1" drywall liners using friction fitted H shaped studs
3/4" air space
2x4 studs at 24" o.c.
1/2" drywall
Now, to me, this is one common 2 hour rated wall assembly where no plumbing or mechanical duct or equipment can be installed in either inside cavity.
Thoughts?
link to UL website for configuration A and B
https://iq.ulprospector.com/en/profile?e=14938
link to Georgia Pacific for only Configuration B
https://www.buildgp.com/assembly/area-separation-wall-2/
Configuration A shown as:
1/2" drywall
2x4 studs at 24" o.c.
3/4" air space
(2) 1" drywall liners using friction fitted H shaped studs
2x4 studs at 24" o.c.
3/4" air space
(2) 1" drywall liners using friction fitted H shaped studs