I thought we kept behind the timesPapio Bldg Dept said:2000 edition if it is Nebraska
So who wins out if there is a conflict between sfm and Bo???Papio Bldg Dept said:We take the cake on that one...We usually defer preliminary reviews until after they have met with sfm because the two codes just don't match up. Few Nebraska jurisdictions have an sfm for in house reviews. Most require an independent 2000 edition review through the sfm state office, and the sfm has recently taken the position that they don't really care if an IBC AHJ issues a C of O prior to their final inspection. Other than that the locals are great to work with.
IMO, it's not really a matter of vehicles being parked in therewhen the business is closed, but maybe while the business is open........In"Do they really think cars will be parked there during closed hours?"
so if it was open on three sides , put still attached to the building, would you need heartburn medicine???north star said:+ = +RLGA asked:
an enclosed building with vehicles, humans, petroleum & alcohol products
tends to be a dangerous mix, just begging for an ignition source.
[ Example: Dick & Jane roll in to purchase some `shine.........Possibly
their sled is already overheating and not running too well......It stalls
out inside the Liquor Dispensary and catches fire, ...possibly from
faulty electrical wiring, or from Dick & Jane having a rolling meth
lab in the rig with them......Either way, now there's a fire event
inside the building ]...Essentially, I do not know if I would disagree
with the SFM......I WOULD however try to come to some sort of
reasonable design solution, ...if possible!......Just sayin' that
unintentional vehicle fires DO occur inside of buildings, and this
particular project needs to be looked at a little more closely.
No disrespect intended or aimed at anyone!
cda said:if you wind up requireing rated glass appears 8.2.3.2.2 allows an alternative, and I thought I heard that it is now accepted to wet non rated glass, in place of rated glass:ne ciites approach::
http://www.sjfd.org/FirePrev/water_wall.pdf
Beat me too it. You have the sprinkler system so it makes sense but if you didn't, how about fire shutters that cover the glass? Had a large glass wall that was also a seperation wall, instead of fire glass, shutters were specified and installed, triggered by heat sensors and also tied into the fire alarm panel.
Ask for code numbers, no code reference...not enforceable. This FM has to have someone that signs his paycheck.
6.1.14.1.3* Where incidental to another occupancy, areas used as follows shall be permitted to be considered part of the predominant occupancy and shall be subject to the provisions of the Code that apply to the predominant occupancy:
This would allow the open air drive thru and associated “occupied” vehicles awaiting goods as part of the mercantile occupancy. They are not stored nor are they un-occupied or stationary making it a “parking structure” as defined in 101……(1) Mercantile, business, industrial, or storage use
The “Hazard of Contents” area of the code is one often used by myself and others to gain greater levels of protection for situations that have the potential to present greater risk and that may not be specifically prescribed for in the building code.6.2.1.3* For the purpose of this Code, where different degrees of hazard of contents exist in different parts of a building or structure, the most hazardous shall govern the classification, unless hazardous areas are separated or protected as specified in Section 8.7 and the applicable sections of Chapters 11 through 43.
36.3.2.2* High Hazard Contents Areas. High hazard contents areas, as classified in Section 6.2, shall meet all of the following criteria:
Now with that all being noted; I agree with the probability that there could be a car fire in the drive thru but this potential could exist at the exterior and or in proximity to any number of mercantile situations and occupancies. Personally, I would assure there was adequate egress from the convenience store area, drive thru and the facility had plenty of portable extinguishing capability and move on to the next one……choose your battles wisely.(1) The area shall be separated from other parts of the building by fire barriers having a minimum 1-hour fire resistance rating, with all openings therein protected by self-closing fire door assemblies having a minimum 3/4-hour fire protection rating.
(2) The area shall be protected by an automatic extinguishing system in accordance with 9.7.1.1(1) or 9.7.1.2.
(3) In high hazard areas, all vertical openings shall be enclosed.
The SFM is usually the most restrictive, so they almost always win out on that technicality, but when we console ourselves en masse on friday afternoons, we claim to be the winners of diminutive moral victories.cda said:So who wins out if there is a conflict between sfm and Bo???