linnrg
Sawhorse
Can some one please assist in describing the history of the rear grab bars purpose. I have an instance where the rear grab bar and the flush controls (automatic eye type) are in conflict with the 1 1/2" clearance requirements. Also if 604.5.2 allows for the bar to be split why would the clearance be an issue?
604.5.2 Rear Wall. The rear wall grab bar shall be 36 inches (915 mm) long minimum and extend from the centerline of the water closet 12 inches (305 mm) minimum on one side and 24 inches (610 mm) minimum on the other side.
EXCEPTIONS: 1. The rear grab bar shall be permitted to be 24 inches (610 mm) long minimum, centered on the water closet, where wall space does not permit a length of 36 inches (915 mm) minimum due to the location of a recessed fixture adjacent to the water closet.
2. Where an administrative authority requires flush controls for flush valves to be located in a position that conflicts with the location of the rear grab bar, then the rear grab bar shall be permitted to be split or shifted to the open side of the toilet area.
Figure 604.5.2
Rear Wall Grab Bar at Water Closets
609.3 Spacing. The space between the wall and the grab bar shall be 11/2 inches (38 mm). The space between the grab bar and projecting objects below and at the ends of the grab bar shall be 11/2 inches (38 mm) minimum. The space between the grab bar and projecting objects above the grab bar shall be 12 inches (305 mm) minimum.
EXCEPTIONS:
1. The space between the grab bars and shower controls, shower fittings, and other grab bars above the grab bar shall be permitted to be 11/2 inches (38 mm) minimum.
2. Recessed dispensers projecting from the wall 1/4 inch (6.4 mm) maximum measured from the face of the dispenser and complying with Section 604.7 shall be permitted within the 12-inch (305 mm) space above and the 11/2 inch (38 mm) spaces below and at the ends of the grab bar.
604.5.2 Rear Wall. The rear wall grab bar shall be 36 inches (915 mm) long minimum and extend from the centerline of the water closet 12 inches (305 mm) minimum on one side and 24 inches (610 mm) minimum on the other side.
EXCEPTIONS: 1. The rear grab bar shall be permitted to be 24 inches (610 mm) long minimum, centered on the water closet, where wall space does not permit a length of 36 inches (915 mm) minimum due to the location of a recessed fixture adjacent to the water closet.
2. Where an administrative authority requires flush controls for flush valves to be located in a position that conflicts with the location of the rear grab bar, then the rear grab bar shall be permitted to be split or shifted to the open side of the toilet area.
Figure 604.5.2
Rear Wall Grab Bar at Water Closets
609.3 Spacing. The space between the wall and the grab bar shall be 11/2 inches (38 mm). The space between the grab bar and projecting objects below and at the ends of the grab bar shall be 11/2 inches (38 mm) minimum. The space between the grab bar and projecting objects above the grab bar shall be 12 inches (305 mm) minimum.
EXCEPTIONS:
1. The space between the grab bars and shower controls, shower fittings, and other grab bars above the grab bar shall be permitted to be 11/2 inches (38 mm) minimum.
2. Recessed dispensers projecting from the wall 1/4 inch (6.4 mm) maximum measured from the face of the dispenser and complying with Section 604.7 shall be permitted within the 12-inch (305 mm) space above and the 11/2 inch (38 mm) spaces below and at the ends of the grab bar.