What is the UL rating on the fixture?Pcinspector1 said:There will be a neon beer sign behind a fixed cooler glass in the walkin with the plug-cord outlet above, I had concerns that it may be considered a wet location but can't fine an NEC requirement that it has to be protected by GFCI outlets or weatherproof covers for condensation. just wandering?
Above where? Refer to Article 400.8 in the 2008 NEC."There will be a neon beer sign behind a fixed cooler glass in the walkin with the plug-cord outlet above,..."
Good Luck....Pcinspector1 said:Mark, I think 314.15 (a) will do! Thanks!
peach said:if it's not a dry location, it's something else and GFCI is required.
Do you have a code section to back up the requirement for GFCI protection in a walk-in cooler?Builder Bob said:GFCI yes..... and also remember article 300.7(A)