Hi Guys,
I'm designing for a mechanical for this hotel which has a parking and I assumed that the garage was open because the architect told us so. I did not provide ventilation for the garage because code says it is not required. Now, I just received correction from the city to demonstrate and document that the parking garage complies with 406.5.1 to 406.5.11. The 2019 California Building Code outlines what defines an “open” parking garage in Section 406.5.2:
I'm designing for a mechanical for this hotel which has a parking and I assumed that the garage was open because the architect told us so. I did not provide ventilation for the garage because code says it is not required. Now, I just received correction from the city to demonstrate and document that the parking garage complies with 406.5.1 to 406.5.11. The 2019 California Building Code outlines what defines an “open” parking garage in Section 406.5.2:
- Exterior side of the structure shall have uniformly distributed openings on two or more sides
- Area of these openings shall be at least 20% of the total perimeter wall area of each tier
- Aggregate length of the openings shall be at least 40% of the perimeter of the tier (Exception: Not required if openings are uniformly distributed over two opposing sides of the building