• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Reinforcement coverage

darcar

Silver Member
Joined
Nov 12, 2009
Messages
129
I had this issue when I recently tested for my IBC Commercial Inspector and now its surfacing in a real life senerio...

I'm looking for how much coverage is required for reinforcement in the 2009 IBC...

Section 1907.5 states that depth, coverage etc. shall comply with ACI 318 Section 7.5... section 7.5 of the concrete manual is a section that addresses BLENDED HYDRAULIC CEMENTS ...?...(I purchased the 2009 IBC and ACI 318-08)

I had several questions for my test that were directed to the concrete manual, and the sections didn't coincide with the topic or question at hand

Any thoughts?...
 
forget it... I figured it out.

I misunderstood and bought the CONCRETE MANUAL when in reality I needed the BUILDING CODE REQUIREMENTS FOR STRUCTURAL CONCRETE...this was not clear and feel like the CASH COW that is the ICC has mislead me and tricked me into purchasing a book that I didnt need!

Buyer beware
 
darcar,

Would you please share your results of how much coverage is required, and the applicable

code section?

Thanks!

.
 
globe trekker said:
darcar,Would you please share your results of how much coverage is required, and the applicable

code section?

Thanks!

.
As soon as the book arrives :)
 
looking at the "Manual" it appears the req depends on if its a footing or wall.

Wall clearances req 3/4" to inside face, and 1-1/2" to outside face.

2" clearance to bar ends

3/8" if depth is 8" or less and 1/2" if >8" depth...

its kind of hard to understand the tables
 
Back
Top