In order to remodel a multi-stall restroom to make it accessible, it is very common that the solution requires removing at least one toilet, and often a lavatory as well, in order to create enough space for the accessible toilet stall.
So this is in conflict with the plumbing code required minimum number of fixtures. I am in CA, so I refer to CPC 422.0 Minimum Number of Required Fixtures.
Say I am remodeling restrooms that serve an auditorium. The women's currently has 6 toilets and 4 lavs. If I calc'ed it out per today's code it would comply with minimums, just exactly.
But in order to make that restroom accessible I have to pull out 1 toilet and 2 lavs, leaving the restroom short. Technically I could enlarge the restroom, but that would be quite an insane cost burden and would have a dramatic impact on multiple adjacent spaces.
So, how do you address this situation?