Replacing batt insulation between rafters.

Joined
Oct 19, 2009
Messages
525
Location
Lincoln
Given:
2018 IECC and project is located in climate zone 5A.
Minor remodel to an existing three story apartment building. It is non-substantial because the cost of the remodel ($20,000) is less than 50% of the overall value of the apartment building. And the energy use of the building is not being increased.
Plans were thoroughly review and approved during the permit application process.
The building inspector sees that the building owner is removing the old R13 batt insulation and replacing it with new R13 batt insulation.

Question:
Section C503 states that existing ceiling cavity need not comply with the requirements of new construction provided that these cavities are filled with insulation. Is it acceptable for the new insulation to be equal to the existing insulation but less than the prescribed value of R38?

As always, thanks in advance.

ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
 
Roof/ceiling gets tough as there is typically room to add, were the cavities exposed?

Exception: The following alterations need not comply
with the requirements for new construction, provided the
energy use of the building is not increased:
1. Storm windows installed over existing fenestration.
2. Surface-applied window film installed on existing
single-pane fenestration assemblies reducing solar
heat gain, provided the code does not require the
glazing or fenestration to be replaced.
3. Existing ceiling, wall or floor cavities exposed during
construction, provided that these cavities are
filled with insulation.
4. Construction where the existing roof, wall or floor
cavity is not exposed.


If they were not exposed AND the energy is not increased, no upgrade required....
 
Most of the cost is the labor, which they are already spending. Should have been a very minor upcharge to increase the insulation.

Looking at home depot, r13 is $0.44/sf and r38 is $1.59. You’re saying they couldn’t afford $1/sf more?
 
  • Like
Reactions: ICE
Most of the cost is the labor, which they are already spending. Should have been a very minor upcharge to increase the insulation.

Looking at home depot, r13 is $0.44/sf and r38 is $1.59. You’re saying they couldn’t afford $1/sf more?
I'd say a 200% increase is a lot more....
 
"Cathedral batt insulation gets it up to R30."

But you need 2 x 12 joists or rafters (and probably add baffles) to get the necessary air space if there is no attic space.
 