There are no EGCs in the meter enclosure unless the meter is downstream of the service disconnect, which most POCOs wouldn't allow. The MBJ has to be in the service disconnect, and that is the origin of the EGC system.It was a learning curve for me when I first saw the EGC connected to all meters.
But a GEC can be terminated in a meter enclosure if the POCO rules allow. Or any other location between the service point and the service disconnect.
Cheers, Wayne